I have a question which is slightly unrelated to the main topic of this thread (sorry OP). If one has to choose between getting a dedicated line or a good power conditioner, which one provides the biggest bang for the buck. If the answer is 'both', which one should you get first?
Dedicated power
I'm looking to run a dedicated 30a and dedicated 20a line to my system directly from the fuse box.
I currently have some florescent lights and some other junk on the line so I'm hoping it will be an improvement. Things sounds like they are straining somewhat when you crank things up. The amp will go on the 30a line and the digital stuff on the 20a.
Anyone done this and saw improvements?
I currently have some florescent lights and some other junk on the line so I'm hoping it will be an improvement. Things sounds like they are straining somewhat when you crank things up. The amp will go on the 30a line and the digital stuff on the 20a.
Anyone done this and saw improvements?
145 responses Add your response
a forceful foot pedal hit on a bass drum.Exactly what is shown here http://ielogical.com/assets/CblSnkOil/Signal_vs_ACLine.png The drum transient occurs right in the middle of the negative A/C signal and the wire is supplying ZERO current to the +ve PSU filter bank and will continue to supply zero current until the line voltage rises above the filter bank voltage X the power transformer ratio. At that time a large current spike will charge the caps. However that spike is well below the line capacity. Examine the "White Rabbit" track. The signal oscillates either side of 0v through the entire A/C line wave cycle. The filter caps are only charged when it is their turn on their half of the A/C cycle. Rock music has about a 20db dynamic range or 100:1 power ratio. So a 500W amp is putting out a fraction of its total capability. The ONLY time anywhere the line ampacity is required is when driving a load resistor. Voltage, length of the wiring X 2 and the gauge of the wire used. I covered that in Headroom Loss for 1600w on 14ga/120v | Audiogon Discussion Forum Upping the gauge from 14 to 10 results in a 170mΩ decrease in wire resistance over 54 feet. The voltage ratio is 20 * log ( 0.987 / 0.968 ) = 0.169db relative to the unloaded line voltage! see ieLogical CableSnakeOil It's my contention that improvements heard after a 10ga rewire are largely due to direct clean connections and not the wire gauge. If rewiring for audio, go direct and only use screw terminals on quality outlets. My media room has a dozen outlets which were daisy chained with push terminal quick connections. This circuit is used for 2x 600w electric heaters. I'd estimate the length at about 80 feet. I had a 5-6v drop from the first outlet to the last when loaded by both heaters. Removing the quick connects, cleaning the wire and using the screw terminals resulted in under a volt drop when loaded. |
If lights are 'blinking' they are on the same circuit. Sockets and lamps should be wired on separate circuits. Likely there are other high current loads as well. I've been doing this a very long time. Including professional recording studios. 12ga wire and 20A breakers for walls of amplifiers. Main monitors typically 1 x 20A circuit for 4 x 500 watts [250wpc]. Playback on STUN didn't dim the lights [on a separate circuit] or jiggle a peak responding line voltage monitor. On a 14ga 15A circuit with 10 foot run to the socket, I currently have tri-amped speakers - total 315WPC - plus 2 subs 300W each. Speakers are ≈84dB/w/m and peak levels are +100dB. The REAL cannon in Telarc's 1812 barely jiggle the line voltage when measured with a DSO. Amplifier outputs scale to input levels, i.e. NO compression. |
Talked with my friend who is doing the wiring. We are gonna do 220v to a small box very close to where the outlets are going. This should distance the circuit even further from other crap on the lines and only cost about 50 bucks more to do. We did determine today there is gonna need to be a bit more drywall rip up than we initially thought. HATE HATE doing drywall! Ohh well crappy patch job and hang a pic over it. |
Post removed |
Sunfire XTEQ: ¿Que? 2800W is way overload for a 15A breaker, moderate overload for a 20A. It's enough to cause a breaker grief, particularly an aged one. One thought, what are the street input connections like? I've seen some really horrible stuff in the meter and into the box. |
ieales742 posts02-08-2021 11:32amIn my shop (not my music room), I have nothing run through the outlets. They aren't wired in series, each is pig-tailed off the 20A circuit(s) running through the boxes. This would seem to me to be advantageous on an audio circuit, as well. Obviously, if you have a dedicated circuit, it's not an issue. |
Post removed |
invalid110 posts Here is a Jon Risch post. It’s in regards to VD on a power cord but it could be used for branch circuit wiring as well. (Jon Risch is a well respected EE ) https://www.audioasylum.com/audio/cables/messages/13538.html This from Nelson Pass. https://www.passlabs.com/technical_article/power-supplies-commentary-for-consumers/ Here is a post from Ralph (M) . Again the subject is for power cord VD. https://www.audioasylum.com/audio/cables/messages/17/174988.html |
Post removed |
Post removed |
Thinking back, these are some of the problems that caused power problems:
|
From the HCA-3500 owner's manual: "Power Requirements 110 Vac-120 Vac 1200 watts per channel" Seems pretty simple to me. I = P/E I = amps (the great debate) P = watts (1200) E = Volts (120) After doing the math, the above statement can be re-written: "Power Requirements 110 Vac-120 Vac 10 amps per channel" Note that the requirement is not conditional. No "continuous" or "peak" modifier. Just a simple statement. Yet, it's amazing how many people will think, "well, if 20 is what the manufacturer recommends, 30 must be better!" Parasound puts that in their literature for a reason. That's what the amp needs. That's all. No more. And I can pretty much guarantee that there is no statement anywhere from Parasound that even hints at running a 30 amp circuit. Because if they did, Parasound then becomes involved in what happens next. Anyone who runs a 30 amp circuit to a 20 amp duplex is an irresponsible fool and creating a fire hazard. 30 amp duplex plugs don't exist for a reason: to prevent someone from doing something stupid like this. So, after their house burns down because they ran too much power to a circuit that wasn't designed for it, the Fire Marshall is going to go to their insurance company and explain what the cause of the fire was. The insurance company is then going to say to the homeowner, "Son, you're on your own." So, the bottom line: Do Not run a 30 amp circuit for something that was not designed for it. |
ieales"both a recording studio and a mastering lab had issues from underground transformers" I have never heard of such a thing are these transformers between substation and end user is that allowed in your country? |
jea483,554 posts02-09-2021 10:13am
Same way Sears used to claim they had 6 hp shop vacs. Theoretical number a fraction of a second before the device went up in flames. Shameless marketing. |
ieales"Where all the services are underground, there are vaults with transformers.In my current location we have small above ground transformers every few houses and a large vault with a larger transformer." I understand underground electric service but I have never heard of the transformers themselfs actually being installed underground or what some would call "below grade" and that would be for the reason you mention that it would be subject to the results and effect of flooding. |
Post removed |
jea48"There are at least 5 million of them across the US. They are quite common in large cities in the north. Downtown NYC is full of them. In many cases below the sidewalks in front of buildings. How is water kept out of the vaults? Sump Pumps for one." Thank you very much for this information which I find "suspect" as a matter of practice but it explains a lot the US has a reputation for very unreliable electric service and having now done some Googling on this purely for curiosity I see that flooding has often caused massive power outages sometimes lasting for weeks! |
Very unreliable electric service? Thank you very much for this information, which I find "suspect". Good grief. Flooding has caused a lot of problems, depending on the severity. The solution, of course, would be to not allow anyone to live near any of the thousands of miles of seacoast, nor near any rivers or streams. I think if we displace 50-100 million citizens living along the Mississippi and Missouri drainages, for a start, we can nip this problem in the bud. |
builder3"Very unreliable electric service?Thank you very much for this information, which I find "suspect". Good grief. Flooding has caused a lot of problems, depending on the severity. The solution, of course, would be to not allow anyone to live near any of the thousands of miles of seacoast, nor near any rivers or streams. I think if we displace 50-100 million citizens living along the Mississippi and Missouri drainages, for a start, we can nip this problem in the bud." You are very welcome and might choose to consider that floods are also an ongoing issue across much of the globe including Europe and Scandinavia and yet power outages lasting for weeks on end as a result of flooding just does not happen what you find acceptable electrical service would be considered of "third world" quality in many parts of the world. |
what you find acceptable electrical service would be considered of "third world" quality in many parts of the worldThe City of Los Angeles extracts $¼ BILLION annually from DWP. Hence ZERO maintenance. The pole in my yard was installed in 1962. Ditto the phone wiring. Crackles every time it rains. Pac Bell says the problem is inside the house because there is no crackling when they show up in dry, sunny weather. Sheesh! |
clearthink1,179 posts02-10-2021 8:48amYou are very welcome and might choose to consider that floods are also an ongoing issue across much of the globe including Europe and Scandinavia and yet power outages lasting for weeks on end as a result of flooding just does not happen what you find acceptable electrical service would be considered of "third world" quality in many parts of the world.Well, I did a bit of research before replying. I'd have to say that the big difference is probably that in the U.S., the flooding very often comes hand in hand with some very serious storms. These would be the occasions that people might be without power for extended periods. I couldn't find any record of huge storms in Europe, only the remnants of various hurricanes. I saw some that spoke of 70 mph winds, and 1-2 inches of rain. That would be merely a blustery weekend, here. Most (all?) of the events with extended outages in the U.S. have been the result of horrific storms, hurricanes, or tornadoes with winds in the 130-200mph range, and often rainfall measured in feet. |
Post removed |
builder3"I did a bit of research before replying. I’d have to say that the big difference is probably that in the U.S., the flooding very often comes hand in hand with some very serious storms. These would be the occasions that people might be without power for extended periods. I couldn’t find any record of huge storms in Europe" It is apparent and evident that you are not so good at what you call "research" and you are equally unfamiliar with history and science. It will obviously surprise you to learn that weather is everywhere across the planet and that includes extreme weather the US is not the only place in the world that has extreme weather. If you really thought the US was the only place for floods and other extreme weather you’d think you lead the world on climate change efforts, intitiatives, and programs but instead you come in "dead last" as you say. Blaming two week power outages on weather is like saying that other American excuse "the dog ate my homework." Other posters here have explained the condition of your electric system and it is obviously not good it is "third world" I could tell you more but you wouldn’t believe me. |
builder3 I’d have to say that the big difference is probably that in the U.S., the flooding very often comes hand in hand with some very serious storms. These would be the occasions that people might be without power for extended periods ... Most (all?) of the events with extended outages in the U.S. have been the result of horrific storms, hurricanes, or tornadoes with winds in the 130-200mph range, and often rainfall measured in feet.Nope. I live in an area not especially subject to those conditions and when we lose power it’s not uncommon for the outage to last for two weeks. (To be fair, sometimes it's "only" for two or three days.) The poles and equipment that feed my neighborhood - which has underground service - often date to the mid-40s, according to the crews who repair the work. When repairs are made, the replacement poles and other equipment is to the same spec as the equipment that failed, so it’s sure to fail again. If the electric utility does upgrades in my state, it’s never in my neighborhood. State regulators make promises but can’t show results. My electric utility also suffers from other performance problems, but that’s a bit OT. Many of my neighbors and I consider our electric service to be of third world quality and these power problems have resulted in deaths more than once. It’s pathetic. |
Well finally had the dedicated lines installed. I have to say it sounds denser and cleaner. Better bass definition and whatever little bit of hash in the highs seemed to be diminished. Everything seems tighter and better separated. Obviously this is not a blind test and yes there was/is some bias of wanting to hear an improvement. I have been working out of this room for a year so I listen basically all day long if not on a meeting so I have a pretty good handle on the difference. All I know is it did no harm and I feel like there is a noticeable improvement. I would highly recommend doing this if you don't need to rip a bunch of drywall up for the small investment. A fraction of what some power cords cost. |