Measurements for a dedicated line


The question of whether a homeowner should get a dedicated line is often like "should I get bangs." It’s a little complicated. Here are a couple of reasons to consider not:

I. My experience is that you won’t eliminate all the other noise coming from your home even if you do run a dedicated line. I still hear motors switching on and off despite being on completely different circuits.

II. A little resistance and a little inductance may actually be a good thing in keeping noise out of your line, so overkill on the wire gauge may not help this.

Why you definitely should get a dedicated line, with thicker wiring:

 

Less voltage sag.

 

Voltage sag means that under load the resistance in the line will cause the AC cabling int he wall itself to consume some of the AC voltage, giving your gear less volts to work with. This sag is proportional to current, so the more amps your gear is drawing the more sag.

This sag is something you can measure. There are two things you need to look: The hot to neutral voltage and the neutral to ground.

With nothing on the circuit your N-E (neutral to earth or ground) should be 2V or less. If it’s significantly higher than that stop and call an electrician. That’s true for any circuit in your home. High N-E values are indicators of a problem which may be in the circuit or in the service wiring from outside to the panel.

What happens when you turn your equipment on and play music is that the line will sag. The H-N (hot to neutral) voltage will drop, and the N-E will go up. Some sag as you turn on big amps is normal. So long as you are not tripping breakers you are fine. What you want to measure is the sag after your system has stabilized and while it’s playing music.

Keep an eye on the N-E value, as this will be a good indicator of the sag independent of the incoming line voltage. It may also point out where you may have issues. That is, if you measure an extra 2V of N-E, your sag is probably around 4V, so you went from 120V to 116V and you can be relatively comfortable it isn’t outside influences.

Of course, any good multimeter will work for this but I like plug in meters with built in N-E measurements. This one is cheap, and the N-E may not be hyper accurate, but it is the only device I’ve found on Amazon that will show you both the H-N and N-E voltages at the same time.

The nice thing about any plug-in type voltage meter is you can watch it over  a couple of days without hand holding probes in the socket.

If you find another which does both please post.

 

 

erik_squires

I got the Kaiweets off of Amazon. It is showing a voltage fluctuation between 119 and 122 volts. It is gradual throughout the day. The higher readings tend to be late at night when I favor what is coming out of the system. However, since injectiing the Audions into the picture I can't say I hear as much difference. The previous situation was tube pre and power while at this moment it is just the pre with the tube power amp on the sidelines.

@dpop - A GFCI outlet senses differences in current at the outlet between the hot and neutral. A voltage on the ground won’t cause this, necessarily. A leak between neutral and ground at the appliance connected would.

In fact, GFCI outlets don’t even need a working ground, so can be used to retrofit outlets without a ground conductor.  If all is well, the current flowing from hot and through the neutral back to the panel should be identical.

The theory of voltage differences between neutral and ground is related to whether or not current is flowing.  Since ground should have no current, it should also have the same voltage as at the panel. Neutral on the other hand, when it has current flowing through it, will be lifted from ground by the imperfect resistance of the copper wire.

Ohms Law:

Volts = A * R

So with 1 Amp, and a resistance of 0.1 Ohms you should see Neutral lift to 0.1V above ground.

The ground conductor also follows the same math, but:

Volts = 0 Amps * 5 R = 0 Volts

That is, from one end of the ground to the other is still 0 Volts. 

N-E volts 00 with the microwave on or off

Those figures were all based on using the KAIWEETS tester. I have other DMM’s which are much more accurate. Since I’m discovering my readings are now in the mV range, I won’t be using the KAIWEETS tester for these readings anymore.

You will get the same measurements on a bootleg ground.

I’ve visually inspected my outlets. They don’t have bootleg grounds...make that anywhere in my house. When I first moved in in 2001, I inspected, and changed out every outlet, along with numerous wall switches. I would have never allowed any bootleg grounds if I had encountered them. I would have recognized them even in 2001.

It looks like *this* is the ultimate outlet tester.

Ideal SureTest Circuit Analyzer

You Tube demonstration of Ideal SureTest Circuit Analyzer

jea48 said:

Are you sure you have an Equipment Grounding Conductor at the outlet?

dpop response:

100% most definitely; on both outlets being discussed. I can take my multimeter and read 121.6 volts across the hot and neutral (no load), and the exact same voltage is measured across hot and the EGC.

You will get the same measurements on a bootleg ground.

L to EGC on a bootleg ground is actually from L to neutral.

N to EGC is actually From N to itself. Naturally it will measure 0.00V

What is a Bootleg Ground and Why is it Dangerous?

dpop said:

My microwave oven consumes 14.6 amps during operation (measured using the amprobe meter). Volts available at the outlet with the microwave off was between 121.3 - 121.5. Volts available at the outlet with the microwave on was 117.9. N-E volts 00 with the microwave on or off.

"N-E volts 00 with the microwave on or off. "

Sure sounds like a bootleg ground to me. (Assuming you were making a good solid connection to the N and EGC with your DMM test probes.)

dpop said:

I completely understand VD on hot and neutral. Thanks, but no further explanation is needed on that. My curiosity was always with the N to EGC.

I don’t think you do fully understand L to N VD in a current carrying circuit.

IF you have a VD on a loaded circuit. Actually measured it, (which you did (L to N), then you will, should, have measured the Voltage Drop across the length of the neutral conductor, when you measured for voltage from N to EGC. Can’t have one without the other.

.

Food for thought:

As for the voltage measured from N to EGC. IF the EGC is a solid low resistance/impedance connection with a high level of conductivity then it is assumed to be a good, so called earth ground. Therein at the same zero ground potential as the electrical service main Grounded Conductor, The neutral conductor. (They are Bonded together at the main panel.)

Therefore the way I look at any voltage measured from N to EGC, which is the result of a measured VD across a connected load from the Hot to neutral of a branch circuit, imo, should be considered as an above ground voltage... There’s one to ponder... Any EEs in the house?

.

I remember reading in the NEC (National Electrical Code) years ago there is/was a maximum allowed resistance measured from the neutral conductor to the EGC conductor at the end of a branch circuit. Just going from memory it was not more than 2 ohms or 1 ohm. I’m thinking 1 ohm.

Test:

Branch circuit de-energized. Verify circuit is dead.

For a good test:

Make sure there is not any loads connected to the circuit. Unplug everything from outlets. Check for ceiling lights that may be on the circuit. Make sure light switches are off. Measure for resistance.

I measured for resistance at the two 20 amp dedicated branch circuits in my 2ch audio room. Both measured 000.3 ohms each. (Fluke 87 DMM.)

The two branch circuit are 10/2 NM cable (Romex) 75 ft each from panel to wall outlets.

.

.

Hot-neutral is the load voltage. Voltage should read about 120 V (typically 115 V to 125 V). You measure exactly 118.5 V.

  • Neutral ground is a voltage drop (also called IR drop) caused by load current flowing through the impedance of the white wire. Let’s say you measure 1.5 V.
  • Hot ground can be thought of as the source of voltage available at the receptacle. You read 120.0 V. You note that hot-ground is higher than hot-neutral. In fact, hot-ground is equal to the sum of the hot-neutral and neutral-ground voltages.

Diagnosing Power Problems at the Receptacle - Fluke Corporation

 

Post removed 

@jea48

I completely understand VD on hot and neutral. Thanks, but no further explanation is needed on that. My curiosity was always with the N to EGC. That’s where I’ve been confused all along. I’ve never paid much attention to that measurement. It’s starting to click now (as you’ve raised my awareness), especially after looking at a few websites explaining what to look for. Going forward, I'll be paying closer attention to it in the future. 

Neutral-to-Earth/ground Voltage- Causes, effects, and solution

@dpop,

I ran some tests for VD on a convenience receptacle outlet branch circuit.

Wiring is 12/2 with ground NM cable, (Romex trade name). Length, distance, from panel to wall outlet used for test is approximately 65 ft. Nothing was plugged into any outlet. Nothing but wall outlets on the circuit.

DMM for first test was a Fluke 87.

Load is a 1875 watt hair dryer. Calculated amp draw is 15A @125Vac.

1875W / 125Vac (data name plate) = 15A.

No load, L to N, 123V.

N to EGC measured 3.4mV ( 0.0034V)

With load, L to N, 118.2V... VD, 4.8V.

N to EGC, 2V. (Half of 4.8VD = 2.4V)

/ / / /

2nd test I used a Klein CL800 clamp amp meter. I used this meter because it has two AC voltage switch settings. One works like a regular DMM. Therein it has an internal input resistance is 10megohm or greater. Same as the Fluke 87 DMM.

The other selector switch AC voltage setting is LoZ, (Low Impedance). This setting puts a small load internally across the digital voltmeter circuit. I used the Fluke 87 to measure the resistance of the LoZ setting on the CL800 and measured 3.6K ohms. (3,600 ohms).

.

Test:

Klein CL800. (Meter set to LoZ AC

No load, L to N, 122.5V. .. (I did a quick check with the Fluke 87. It also measured 122.5V.) A point in time...

N to EGC, 0.00V (The Fluke measured 3.4mV ( 0.003V) Ghost Voltage.

With load connected. Hair Dryer same settings.

L to N, 117.8V. VD 4.7V.

N to EGC, 2V. (Half of 4.7VD = 2.35V)

Jim

Post removed 

(I assume the audio branch circuit is 2 wire with ground...)

Correct.

It’s still not clicking in my brain what you’re trying to say about voltage drop across the neutral and EGC. No offense, but if I already have a low impedance EGC, why should I even care about voltage drop, or voltage difference, between the neutral and EGC?

Now draw a symbol for a voltmeter connected from the neutral on the load end of the circuit and connect the other end of the voltmeter to the EGC.

If assuming the load is plugged into one half of a typical duplex wall outlet, and consuming current; you’re saying 1) place the voltmeter on AC volts 2) one probe in the neutral on the other half of the outlet not being used by the load 3) and the other probe touching the EGC. Is that correct? If so, I’ve already tried this before you posted, and the reading is around 28 millivolts. I’ve even tried breaking the EGC connection from the load to the wall outlet, and placing my meter across it - still the same, about 28 millivolts.

BTW, thanks for taking the time to explain this to me. If neutrals were oversized (compared to the hot conductor), would I be seeing less voltage drop in some of my presented scenarios?

 

 

Post removed 
Post removed 

The voltage drop / 2 method only works if the voltage drop is equal.  It is possible the voltage drop is higher on the hot due to resistance. 

Best to measure with a multimeter for the most accurate results.

Are you sure you have an Equipment Grounding Conductor at the outlet?

100% most definitely; on both outlets being discussed. I can take my multimeter and read 121.6 volts across the hot and neutral (no load), and the exact same voltage is measured across hot and the EGC.

Maybe I’m not understanding you correctly, but I’m failing to comprehend why you think there should be some voltage on the EGC for these outlets (under load)? I was always under the impression that the EGC was to keep your equipment as close as possible to ground potential, and provide a safe path for ground-fault current to flow. My thinking is that if there was any voltage on the EGC, and I had in place a GFCI outlet; it would trip.

Post removed 

So, A'gon apparently got upset with me that I said A M A Z O N in an e-mail.  Sheesh! :D

Unfortunately, it's a random draw with this one. Mine was within 1-2 volts. Others have reported as the poster in the thread did, that some can be much more off than that. Good news is [filtered] allows free returns. They do make other meters which get better ratings on reliability, but I dont' know of any that include the Neutral to Earth measurement standard.

So when I came home yesterday evening my Kaiweets Outlet Tester I ordered from Amazon was waiting(love their next-day delivery) for me and couldn’t wait to try it. I’ll be dropping it off at Whole Foods today as it measured an astonishing 17 volts low. Measured with my Fluke 87 and Sperry both measured accurately within a fraction of a volt of each other. Too bad as it is a cool little device, now if only Fluke, Klein, etc., manufacture one of these.  I did see a very nice Klein voltage tester that while doesn't the voltage drop, it's an easy to read  tool for checking correct wiring on a large screen that has a memory when unplugged from the circuit.  With a Non-Contact Voltage Tester about twice the price.  Checkout the videos 

  

 

When I built my house, I had two dedicated lines wired with 10/2 gauge with ground, both going to hospital grade receptacles. Each one is connected to the same buss side at the breaker box. I’ve never heard any noise except a fluorescent light starter in my room where I store cables etc. I replaced it with a solid state starter which corrected the problem. All other low amperage equipment is connected to another line that are daisy chained. The two dedicated lines power two Krell FV-600 monoblocks. 

AC voltage, harmonic distortion and line frequency are all measurable

 

Indeed, but most of us can only measure AC voltage.  Harmonic distortion is definitely not something you get with your average multimeter, and the one thing I have the most faith in is the AC frequency.  So in the absence of anything else, it would be nice to correlate AC voltage with listening experience.

AC voltage, harmonic distortion and line frequency are all measurable. If there is a difference between night and day listening, and it's related to power delivery, we should be able to measure it. Personally I think some of this is psychological. Evening and night time listening hours are typically environmentally quieter, and your brain possibly adjusts to this. I've personally never measured any difference in power quality in my home environment between daytime listening and night time listening. One of my main listening rooms is down in my basement. The environment is intentionally blacked out all of the time (of course except when I light it), so that if this is a psychological thing, I can have a "night" environment whenever I want it. 

When I was a Radio Broadcast Engineer, I had a rack full of equipment in a transmitter room. This rack contained the audio processor for the FM transmitter. It created the audio signature of the FM station. The rack of equipment had a 20 plug power strip, and it was almost full. I plugged in my Fluke 43B Power analyzer, and discovered the Harmonic Distortion for this power strip was 0.0%. I kid you not. I was never able to find another AC plug that ever gave me that low of a Harmonic Distortion reading. The 3 phase power transformer for the building was on a pole right outside the door to this transmitter room.  

@bolong It would be nice if you got a plug - in V meter and could look at it during the day and night to see if you have better voltage at night.  I'd be really curious.

It's not component noise based on what I am not hearing through my horns. If it's noise or voltage on the lines I have no way of knowing that.

My dedicated line made a big difference in system sound quality, but still it sounds best after midnight and into the witching hours.

@dpop The specs seem nice. One of the major issues with WHSP units is the high clamping voltage. The other is activation time. Another is the ability for a surge current to be induced by the AC wiring in the house.

For all these reasons, I still protect anything sensitive and/or expensive with a Furman or Tripp Lite at the outlets.

Still, I have sunk a lot of money into the advanced breakers, home automation, GFCI outlets and fire alarms in this house, so the WHSP unit in my panel is very worthwhile.

I too have whole house surge suppression (never lost anything from storm damage the entire time I lived at this location - going on 23 years now), but since I have so much money wrapped up in audio, video and AC isolation and filtering gear, I sometimes contemplate spending the money on a higher quality surge protector. 

Sine Control Technology

@dpop Sounds good!!

GFCI outlets are cheaper ($20), but if it's not in a convenient location to reset when it trips then a new combination breaker is the way to go.

I also have Siemens.  My panel used 100% Siemens breakers, that were 15 years old when I moved in.  My neighbor had a weird assortment of breaker brands in hers.  I've replaced 100% of the single pole breakers and added a whole-house surge suppressor.  It makes me feel better, but I still lost a laptop in a storm that had no other surge protector on it.

I have a dual gang countertop outlet that has a GFCI outlet in it. It is then connected to, and protects the outlet right next to it. The microwave is across the room, and isn’t within 6 feet of the kitchen sink. When I first moved in in 2001, I inspected and replaced all of the outlets in the house. When I changed out the pizza oven outlet, the insulation on the wires was cracking, and I told myself I hope I don’t have to replace this outlet for a long time after that - so I won’t be switching that outlet to a GFCI. Since we’re discussing this, I’ll probably change out the current AFCI circuit breaker for the microwave/pizza oven circuit with the combo CAFCI/GFCI type (I have a Siemens load center). Having been an apartment maintenance guy for over 10 years, we too never installed GFCI’s for refrigerators. 

My house was built in 1942, and the pizza oven wiring has never been updated, except with a new outlet at some point.

@dpop

Ahhh! Yeah, you can’t do that today. The microwave gets it’s own circuit, which as of 2023 has to be CAFCI and GFCI protected.

Within the past 10 years I updated that microwave/pizza oven circuit breaker to the recent AFCI type.

Nice! Please make sure that all your kitchen counter top circuits are GFCI protected as well. Not sure if an outlet or updated breaker will be the most convenient for you in this case. Leave the fridge alone though, those trip GFCIs all the time. GFCI for kitchen counter top outlets has been code for decades but the latest 2023 NEC code expands GFCI to the dishwasher, microwave, and washer/dryer combos. I’m not sure you need to go that crazy, but I do think it’s worth the GFCI outlets on the counter tops for sure, and any outlets under a kitchen counter as well.

If you buy more GFCI outlets, any major brand but Leviton seem to have high trust factors with online electricians.

 

@erik_squires Good point Erik. I have a Panini maker which is rather light in weight, and easier to relocate vs. my pizza oven or microwave. It consumes 11.8 amps (the pizza oven consumes 11.5 amps). I plugged it into my 10 AWG main audio feed AC outlet. Volts available at the outlet at that moment was 121.8. Volts available with the Panini maker on was 119.0 (a voltage drop of -2.8 volts). N-E volts was 00.

I knew the 10 AWG feed was about 15 feet in length from the circuit breaker box to the measuring point. My other AC circuit feeds for my microwave and pizza oven I discovered are on the same 20 amp circuit as each other (good thing I never have a reason to run the pizza oven and microwave at the same time). The pizza oven and microwave are on a completely different circuit than my 10 AWG AC feed. My house was built in 1942, and the pizza oven wiring has never been updated, except with a new outlet at some point. The microwave outlet was installed at a later date, with copper wiring. The previous owners of the house had that installed. It was tied into the same circuit as the pizza oven outlet. Within the past 10 years I updated that microwave/pizza oven circuit breaker to the recent AFCI type. I’m guessing the wire run to the pizza oven outlet is around 20 feet, and the microwave outlet is 30 feet. Suffice to say there was more voltage drop at the pizza oven outlet (consuming roughly the same amount of amps as the panini maker), at -3.7 volts, than there was at my dedicated 10 AWG feed (-2.8 volts), consuming roughly the same amount of current.

Some of this was eye-opening, as I didn’t anticipate I would see that amount of voltage drop with high current demand at my 10 AWG feed, only 15 feet away from the circuit breaker box. One thing is for sure, I would not want to have any audio components on a microwave or pizza oven circuit when they would be in use.

@dpop Excellent investigations!! :)  While I applaud your work, should also point out how few amps you are drawing is contributing to the stability of the voltage. Your wiring could handle 30 Amps, and you are drawing 2 at peak usage. 

Audiophiles should evaluate the potential benefits vs. costs.  The longer the circuit from the main panel, the more the power draw is, the more worthwhile a dedicated, large gauge circuit becomes.

Using the KAIWEETS KM117B Socket Tester (the one @erik_squires linked), I took some measurements around my home:

My pizza oven consumes 11.5 amps during operation (measured using my
Amprobe ACD-10 TRMS-PLUS meter). With the oven off, AC volts available at the outlet is 121.3 - 121.5. With the oven on, volts available at the outlet dropped to 117.8. N-E volts 00 with the oven on or off.

My microwave oven consumes 14.6 amps during operation (measured using the amprobe meter). Volts available at the outlet with the microwave off was between 121.3 - 121.5. Volts available at the outlet with the microwave on was 117.9. N-E volts 00 with the microwave on or off.

My main audio system is a 3 power amp tri-amped system. The power amps alone consume about 1.5 amps total powered on with no program material. AC volts at the outlet is 121.5 with the amps off. With the amps on, volts at the outlet are 121.0. Peak amps measured at loudest passage was 1.9 amps (or, 0.40 amps above powered up status). The feed is 15' of 10 AWG directly from the circuit breaker box. N-E volts was 00 with the amps on or off.

My furnace consumes 3.79 amps with the unit in full operation (gas burner heating, and forced air fan blowing). Volts available at the outlet with the furnace off was 121.5. Volts available with the furnace full on was 120.5. N-E volts was 00 with the furnace on or off. 

What this does prove to me is how important a dedicated run *is* for power amps, or high current consuming integrated amps or receivers. 

@dpop Those are certainly popular, and I believe the original.  There are now dozens of watt / voltage meters out there, with a variety of smart features, including wifi connectivity.  What I've yet to find is one that measures N-E at the same time as the V.  Still, being able to chart your V over a week can really help you understand your power issues.

Another plug in voltmeter that I really like is the Kill A Watt EZ meter. It measures a lot of things, but the voltmeter portion (which reads in tenths) is extremely accurate. 

Kill-A-Watt(Tm) Ez

@erik_squires you definitely got the quasi dedicated correct…. bummer…. Stromtank… and $ or € can fix that…..

Best to all in the quest for juice, AND clean juice….

I received the test meter today that @erik_squires linked. Right off the bat I would say I’m impressed by its performance. One thing I look for in an AC voltmeter is how quickly it can measure and display voltage drops or variations. Even at ear splitting levels, one of my systems rarely consumes more than 1.5 amps on peaks, so I did not test it there, yet, as I doubt I’ll see much if any voltage fluctuation (10 AWG wire run about 15 feet from the load center). I did however put it on a variac, while quickly adjusting the power, simulating a huge momentary current draw on the line. The meter responded very quickly to this adjustment. All outlets that I’ve plugged it into so far are displaying 00 volts for the N-E figure. I am fortunate that I am fed directly from the step down transformer on the pole (I’m not at the end of the line) for my block. Even at that, during heavy summer cooling periods, I may see my total house voltage temporarily (for a few hours) drop about 2 volts. The meter doesn’t display tenths of volts for the L-N display, but using a reputable Fluke, the reading was only off by less than 1 volt. I would say it was easily worth the (roughly) $20 purchase price. My house voltage (on one leg I constantly monitor) typically remains at 120.7 volts 99% of the year.

Yes, I do have good power. Part lucky, part by design. The only loads I have in the house of stereo other than audio equipment are lighting and a Daikin Whisper Quiet AC/heat wall unit. Therefore a very constant feed no matter if it's all running or not. Simplicity is the key in this instance.

Just so readers understand, when a circuit has no load on it you are looking at the best case scenario.  Running a dedicated line won't get you better than that.

Where a dedicated line improves things is in the case of a circuit with load.  Less load + thicker cables should reduce voltage sag.

Point is, you can't do better than the panel voltage, and if it's going up and down, your dedicated circuit won't magically improve upon that.

@baylinor You have really good house power! I have a quasi-dedicated circuit. It runs the HT and a USB house camera on it. I still have more fluctuations in voltage than that, even with nothing on. Typical voltages, with an unused circuit (except USB camera) runs 115-123V and my heat pumps and air handlers definitely move that needle as do the seasons.  BTW, I live in an area served by pad mounted transformers and underground feeds, so it should be relatively stable compared to pole mounted power.

I use a Furman voltage regulator as the "front-end" to my power conditioners to ensure the power is even tighter even when running the full system.

Dedicated power feed to house of stereo here with plug-in volt meter always displaying voltage. Always reading between 121 and 124 volts in dead of Summer or dead of winter. Not sure about the electrical specific points raised by Eric but a dedicated power feed has been a huge plus in my case. By example, my main house right next to it can fluctuate between 114 and 124 volts.

Combining, or "sharing" the Neutral Leg (white wire) can cause an imbalance of a voltage on the Neutral Leg. When a homeowner, or their "handy man" add an outlet, or a light fixture, or another modification to the home wiring, it is tempting to attach the modification to an existing circuit. It is not unusual to find a junction box with multiple neutral wires all connected together. The Neutral Leg has a relationship to Ground, but it is not to be treated like a ground. Stray voltage on the neutral can damage sensitive electronics, especially equipment, like computers, and electronics that operate on a reduced voltage (a power supply transformer is an indicator, which includes wall warts). Voltage on a neutral can indicate a problem out side of the distribution panel, yes. But more often it indicates wiring errors within the home. Stray voltage on the neutral is a problem, but usually it is a symptom of a problem with the basic wiring not being NEC (National Electrical Code, or NFPA 70) "Code" compliant. A separate distribution panel for your listening room does have some advantages, but it needs research and design to be of a true benefit. A qualified Master Electrician can, and should, inspect your wiring and panel for defects and deficiencies before proceeding. In older homes the wiring and protection (circuit breakers age, for example, and wiring and devices may be out of date and improper) may not be in compliance with current NEC "Code" requirements. It is worthwhile having a Licensed Master Electrician (there is stringent and frequent testing involved in moving from Apprentice, through Journeyman to Master. You don't get to self assign that title and award yourself a license) inspect the electrical service in your home and review with you a course of action, if needed. For less than the cost of a "power conditioner" you can have some certainty about the true condition about the quality of the electricity in your home. And then you can make an informed decision on how to proceed.

@audioguy85  I did exactly the same thing, only my main floor run was 30 feet, and my basement system was 20 feet. I use a Cardas Audio 4181 receptacles. Same result Zero noise, larger soundstage, and more definition.

I have a dedicated line and hear no such noise or interference from other circuits, motors etc  it also was not expensive or that difficult. I also did not go nuts, no need to. Simple 12 awg romex 50ft, 20 amp breaker, AQ nrg Edison receptacle. Sounds great, no noise that I can hear, and provides enough power to my class A sugden and all the rest. Did it myself to boot. 

The neutral should have no more than 2 volts to ground. If you have more than that (as measured at the receptacle) the first thing to do is to go to all the outlets with a plug in receptacle tester and make sure they all read ’wired correctly’ and none read 'open ground', in which case call an electrician.

If the receptacles are okay, go to the panel and check to see if there is the same voltage between the neutral and ground bus or neutral and panel bond. If it is the same then that is pretty much the resistance to ground causing the neutral voltage. Check the panel bonds to both the panel and the ground rod.

If the voltage between G-N buss bars is a lot less than measured at the receptacles, then the most likely culprit is a loose connection somewhere in the circuit. First tighten all the lugs on the neutral and ground bars (a lot of times this will fix it). If that doesn’t do it then you have to trace the circuit for j-boxes and check or replace the wire nuts, then work your way to each receptacle and check the pigtails. If you have the backstab connectors, those too are a source of resistance.

Somewhere along the line a loose connection places a high impedance on the neutral creating a voltage divider, which shows as a few volts on the neutral.

If you are doing a dedicated line, there's a couple of interesting alternatives.  Getting a sub panel, and running 240V instead of 120V.

A sub panel means you run say 6 gauge wiring up to your listening room and then use short 12 gauge runs to each outlet.  Since you have 6 gauge wiring, your overall voltage sag is going to be negligible.

Another alternative is to run 240V and use a balanced power conditioner to step it down.  Again, you cut the current in half, therefore the sag is halved.

@erik_squires Thanks for the insight.  Yes, my PP10 is the original and the PP12 replaced it.  Even Paul once kindof ruminated that the PP10 might be the better option, especially for amps.  

Too bad about Jensen.  PS Audio is tough competition. but I'd like to see another option for the old school design.

Jerry

 

@carlsbad2 Honestly haven't kept up with them that closely.  I remember there was an original generation that was essentially using linear amplifiers, then they switched to Class D.

At the same time the founder of Jensen Transformers (really nice guy) founded another power conditioning company, Perfect Power?  Forgot the exact name, that used buck/boost transformers.  Very efficient compared to the PP, but still based on a linear amp.  Sadly that didn't really go anywhere. Sounded like an excellent compromise IMHO.