Yes. Your breaker is failing. They use a magnetic principle and the more they break, the easier they break. Replace it- see how that goes.
Amp tripping circuit breaker.
I have a 20 amp circuit, AFCI breaker, with only my entertainment rack on it. The breaker has been tripping periodically for about a year now. Recently the problem has been worse and I suspected my amplifier. Long story short, the breaker only trips when the amp is plugged in, with statistical certainty. Unknown if it matters if amp is on or not.
Amp is a Monolith 7. I opened the cover and saw no obvious signs of damage. Everything is clean and dust free.
any thoughts?
Amp is a Monolith 7. I opened the cover and saw no obvious signs of damage. Everything is clean and dust free.
any thoughts?
24 responses Add your response
One thing I forgot to mention - the reason I suspected the amp is because it’s own protection was tripping earlier in the summer, often immediately when powering from a cold start. It ended up going away. Only thing I can think of that made the problem go away, was I went from having the thermostat set at 76 to 72, which definitely reduced the indoor humidity. |
Unknown if it matters if amp is on or not.Yes it matters. https://www.youtube.com/watch?v=ihforRdL-TU |
magneplanman OP1 posts Now that’s more info. The breaker on the rear panel is a magnetic type breaker. If it was tripping that could indicate either a short circuit or very high inrush current when the Amp is first turned on. Repeated tripping and you repeatedly resetting it was a bad idea. You may have caused the contacts of the breaker to weld, fuse, themselves together preventing the breaker from tripping open. It looks from what I can tell the breaker is a 15 amp. Now you are causing a 20 amp breaker to trip from a possible short circuit or high inrush current. I suggest you have the Amp checked out. Repeatedly resetting a circuit breaker in an electrical panel can be dangerous. I know of an instance where a 20 amp Square D QO circuit breaker exploded and burned the fingers and hand of an electrician. . |
The AFCI part can trip based on modest ground currents. AFCI is Arc Fault. GFCI is Ground Fault. They are completely different. One is an arc that can be a fire hazard. The other is more a nuisance (when it trips) than a risk. Long story short, the breaker only trips when the amp is plugged in, with statistical certainty. Unknown if it matters if amp is on or not. If it happens with the amp plugged in and turned off there is a statistical certainty its not the amp. the reason I suspected the amp is because it’s own protection was tripping earlier in the summer, often immediately when powering from a cold start. And yet this did not trip the breaker. This is what we call a "clue". It ended up going away.So the amp was a Walker? Only thing I can think of that made the problem go away, was I went from having the thermostat set at 76 to 72, which definitely reduced the indoor humidity. Fascinating. |
@OP By chance is the electrical panel/ AFCI breaker in the panel a Square D type? By chance does it have a white test push button? If so it is a CAFI AFCI and you can test whether the breaker is tripping on over load or short circuit, or, if it is tripping on arc fault. Video https://www.youtube.com/watch?v=Rw8exWpipJY Here is another Link for a square D CAFI AFCI breaker. Click on the first video on the left hand side of the page. https://www.homedepot.com/p/Square-D-Homeline-20-Amp-Single-Pole-Combination-Arc-Fault-Circuit-Break... *Do not attempt to change out the breaker yourself... Hire an electrician. |
If it happens with the amp plugged in and turned off there is a statistical certainty its not the ampso far that hasn’t happened, since I’ve kept a log And yet this did not trip the breaker. This is what we call a "clue". Are you implying that the amp tripping is an independent issue from the breaker? maybe I’m not following. |
Post removed |
I am a certified electrician. And I believe part of the problem is the AFCI breaker since it is known to be a common problem with them and GFCI types. Also confirm if you are using a 29 amp breaker with at least 12 awg. Wire otherwise you are overloading the circuit with your rack setup. Just because the breaker says 20 doesn't mean the romex in the wall is suitable for such a load. I would find out what the amperage is under load with. Conventional amprobe at the panel. And if you are exceeding 16 amps then you are using more than the breaker can handle for long term use. I would recommend a dedicated circuit with at least 12awg 10 would be best. and have the electrician or yourself balance the loads between your 2 legs at the panel. By moving some wires around to come up with the most balanced load on your hot legs. I have seen tripping on breakers from loose connections both in j boxes and receptacles. And in some cases the wires can overheat and melt before the breakers actually trip. Hope this helps. |
NEVER change 2 things at once. Ground at wall outlet? I can understand lost confidence in the amp, but, the advice to replace the breaker first is the best. If electrician does it, he/she can also test ground, at the panel and at the wall outlet. That will tell you whether it was the ground, breaker, or the amp. IF, after replacing breaker, ground confirmed, with amp connected, turned off, new breaker trips, curious indeed. Test that before electrician leaves. Do you have any other equip you could substitute for amp, to see if problem goes away? IOW, think like an electrician rather than as an audiophile. New amp after circuit confirmation? Always fun. Keep in mind, you won't be able to sell the existing amp unless you confirm it was the breaker, not the amp. Another reason not to change two things at once. |
magneplanman OP4 posts Repeat: One thing I forgot to mention - the reason I suspected the amp is because it’s own protection was tripping earlier in the summer, often immediately when powering from a cold start.@ magneplanman I assume you are referring to the 15 amp "Master Power" On-Off/circuit breaker on the rear panel of the amp. Is that correct? The "Master Power" circuit breaker was tripping immediately when powering from a cold start? See page 6 of manual. E. MASTER POWER:The Master Power switch is used to apply or remove power to the amplifier. By contrast, the Power switch on the front panel is used to switch the amplifier between standby mode and full power on.See page 10. MAIN CIRCUIT BREAKER: The Master Power switch on the rear panel doubles as a circuit breaker. If the circuit breaker trips into the off position, try flipping it back on. If it immediately trips back off, unplug the amplifier from the power source and have it serviced.https://downloads.monoprice.com/files/manuals/14566_Manual_160414.pdf One thing I forgot to mention - the reason I suspected the amp is because it’s own protection was tripping earlier in the summer, often immediately when powering from a cold start. It ended up going away. "It ended up going away. " As in the breaker no longer works? Please respond if the above circuit breaker was the device tripping immediately on a cold start up of the amp.I also would like you to move the "Main Circuit Breaker" (rear panel on the amp) to the off (O) position. Verify in the off position the unit is dead, no power, lights, ect... As for the dedicated branch circuit GFCI breaker that feeds the amp. Going from what you posted it was/is high inrush current draw from the amp that was causing the 15 amp breaker at the amp to trip open. Assumption, the breaker no longer works. The GFCI breaker was next in line to protect the branch circuit wiring. (You never mentioned what manufacturer the electrical panel/breaker is. It would be nice to know) Note. It would be safe to say it is the Thermal-magnetic section of the AFCI breaker that is causing the breaker to trip open. The high inrush current draw of the amp is causing the breaker to trip open. Is the AFCI breaker weaker now after several tripping events than when it was when it first tripped opened? Probably. Will installing a new breaker solve your tripping problem? For a while. Band-aid repair. . |
jetter1,477 posts@jetter In your case you may want to see if the manufacturer of your electrical panel makes a High Magnetic, HM, branch circuit breaker. What is a HM type breaker? What does it do? It allows a greater lag time for inrush current before it will trip. Example of: Square D Standard QO115 and QO120 circuit breakers are manufactured to have a magnetic trip point at approximately 8x to 10x the breaker rating. There are some applications, however, in which a load has an inrush current high enough to cause these standard circuit breakers to trip. Examples of these loads include area lighting for athletic fields, parking lots, or outdoor signs. To allow the high inrush current without tripping the circuit breaker, a high magnetic breaker should be used. These high magnetic breakers breakers have a magnetic trip point set much higher than the standard circuit breakers. They can be identified by the HM suffix on the catalog number (QO115HM). Current production HM breakers are also identified with a "High Magnetic" label on the side of the breaker (see photo).https://www.se.com/us/en/faqs/FA96714/ . |
Thanks for the information jea48, live and learn. I will talk to my electrician about it. I know changing a breaker is a simple thing, but I would rather not mess around with it myself. I do know that when a friend was going to replace the breaker in question, for some reason it was not one of cheaper ones that GE makes. It had something about it that made it a $50+/- variant. |
EDIT: jea483,211 posts Correction: As for the dedicated branch circuit GFCI breaker that feeds the amp. Should read: As for the dedicated branch circuit AFCI breaker that feeds the amp. The GFCI breaker was next in line to protect the branch circuit wiring. Should read: The AFCI breaker was next in line to protect the branch circuit wiring. |