Room will have have 3 dedicated 20 amp home runs for the system using 10 gauge 10/2 romex with ground, terminating with PS audio IG 120v outlets.
terminating with PS audio IG 120v outlets.
@frym
Did you run that by the builder’s electrician? Per NEC you can not install an IG (Isolated Ground) type outlet on a 2 wire with ground NM, (Romex is a trade name), branch circuit. FWIW, An IG outlet would serve no purpose whats so ever connected to the branch circuit wiring. None...
With this set up is there any point in setting up an isolated ground and how do I go about it?
By definition an IG ground wire must be an insulated green color ground wire. The ground wire is connected only to the receptacle outlet IG ground terminal and remains isolated all the way to the EGB, Equipment Ground Bar, in the electrical panel. The IG conductor must be part of the branch circuit cable circuit wiring. (NEC allows the IG ground wire to pass through a sub panel and connect to the Main Electrical Service Equipment Panel, (the sub panel is fed from), and connect to the Grounded Service Entrance Neutral Conductor.)
...Now with that out of the way...
The EGC, (Equipment Grounding Conductor, in the 10/2 with ground will work exactly as the described IG ground wire above provided the EGC is not bonded, connected to a grounded box, or what ever, from the ground terminal on the receptacle outlet to the EGB in the electrical panel. (Which you will have with a true dedicated branch circuit.)
House will have 400 amp service utilizing two 200 amp panels.
Each 200 load center panel will be a sub panel. Approximately how far, distance, is the sub panel, that will feed your three new dedicated branch circuits, from the main electrical service 200 amp breaker?
Approximately how far, distance, are the dedicated branch circuits from the audio room wall outlets to the sub panel? ( Measured, up, down, and around).
It is important the electrician does not run the dedicated circuits through the same bored holes through studs or joists. Nor should they be run along side any other branch circuit wiring through bored holes.
After the three dedicated circuits leave the electrical panel as soon as reasonably possible they should be separated from one another by at least 8"- 12" all the way to the wall outlet boxes. Also avoid running the three dedicated circuits parallel to other branch circuit wiring. Especially LED Lighting circuits as well as circuits with lighting dimmers. These circuits are the worse for inducing Harmonic Noise onto the Dedicated Branch Circuits.
See page 16. Read pages 31 thru 37
FWIW...
You might want to consider using solid core 10/2 with insulated green ground. (Solid core #10 conductors, NOT stranded conductors)...
Aluminum armored MC (Metal Clad) cable. (NOT AC Armored Cable.)
I prefer Aluminum Armored MC cable over NM sheathed cable, (Romex is a Trade Name). Especially if the branch circuit runs are long.
Per NEC you still can use a plastic wall box for the outlet for each dedicated circuit.
Why MC over NM?
Cable construction does a better job of controlling any induced voltage from either of the two current carrying conductors onto the EGC. Better than Romex can. Any induced voltage onto an EGC can cause ground loop hum. Especially on long run branch circuit wiring.
The construction of the three conductors are tightly twisted together in a spiral the entire length of the cable. What keeps them tight against one another is the outer aluminum armor.
Example Of Aluminum Armored 10/2 MC Cable: