danvignau
If you are going to the trouble to add a dedicated circuit, go ahead and use 10 guage wire and a 30 amp breaker. You will never be sorry.I agree that 10 ga. wire is a good idea, but a 30A breaker should only be used if the receptacle itself is also rated at 30A. But they have a different plug configuration than 15A and 20A receptacles, so it's really not a practical solution, unless you want to ignore the NEC and just use 20A receptacles.