@lowrider57 Said:
Understood. We discussed this when you advised me about replacing my meter box and outside line due to corrosion. If you remember, distortion and DC was entering my service panel.
I remember the thread. Harmonic distortion caused by a corroded connection in the meter socket was causing a problem with a piece of audio equipment. Wasn’t it a noisy buzzing, vibrating, power transformer?
I think where I’m confused is from comments in threads about using an "independent" ground rod (or 2) from a subpanel or main panel. My take is that these ground rods are not bonded to the main panel. This doesn’t sound kosher. Is there any reason to use multiple ground rods spread out in the backyard? Yes, I know earth doesn’t possess any magical powers.
Independent, dedicated, isolated, ground rods are dangerous. They violate all electrical safety codes.
NEC 250.54 Auxiliary Grounding Electrodes is one of the dumbest code editions ever. All the additional grounding electrodes do is to provide lightning a direct path into a building’s electrical wiring damaging electronic equipment as it goes on its merry way to the electrical service’s main grounding electrode system back to earth. Lightning loves Auxiliary Grounding Electrodes..
.