BUT, an equipment equipment grounding conductor still must be ran with the feeder conductors and the equipment grounding conductor shall be terminated to the equipment ground bar in the main electrical panel as well connected to the ground bar in the subpanel.
The purpose of an equipment grounding conductor is to provide a low impedance path for ground fault current to return to the source, the utility power transformer, through the service neutral conductor at the electrical service main electrical panel where all equipment grounding conductors are connected to.
Understood. We discussed this when you advised me about replacing my meter box and outside line due to corrosion. If you remember, distortion and DC was entering my service panel.
I think where I'm confused is from comments in threads about using an "independent" ground rod (or 2) from a subpanel or main panel. My take is that these ground rods are not bonded to the main panel. This doesn't sound kosher. Is there any reason to use multiple ground rods spread out in the backyard? Yes, I know earth doesn't possess any magical powers.