@erik_squires said:
In addition to the conversation not really going anywhere, I feel it’s also being less than cordial, so I’m checking out.
LOL, "being less than cordial". LOL
@erik_squires said:
It may help you to understand that the MOV’s in an SPD’s for the most part deliberately CAUSE shorts (series mode an exception) which is why they must be a certain distance from the panel. This ensures the AIR of the breakers isn’t exceeded when they do short.
"It may help you to understand"
I took that as an insult.
.
In addition to the conversation not really going anywhere
The conversation is settled. You were wrong.
You proved you were wrong when you introduced series mode SPDs into the conversation.
@erik_squires said:
@jea48 - Of course, always follow the rules, but the 30’ requirement AFAIK is to avoid excess current that is too high for the AIR (current interrupt rating) of panel breakers.
( should be AIC not AIR).
in response to my post: 03-19-2025 at 03:43pm
The 30ft minimum distance requirement has to do with the fault current rating of the Type 3 SPD . Any idea what the Furman is rated at?
(FYI, It was you that introduced AIR instead of AIC into the conversation. My bad for not catching it and correcting it at the time.
Series mode SPDs blows your above statement out of the water.
.
Best regards,
Jim
.