@signaforce , I sent you a PM through the Agon message system.
The distance (10 meters) is exclusive of the conductors provided with or used to attach SPDs.
AC Power
I have a relatively nice system, but have done nothing with my AC power, with the exception of upgraded PC’s and a cheap iFi plug in power conditioner. My question is multi fold… do I need to do something, and if so what? Dedicated line (15A or 20?)? Quality power conditioner? Both? Which one first? How do you tell?
My system is a combination of HT & 2 channel & I tend to use both simultaneously as I like to watch sports while listening to music.
My amp is (I think) a relatively low draw… Moon 330A, Rythmik sub, BHK pre, Aurender, Qutest w/Sbooster, R11’s. No high power amps are in my future & never listen above 75db. I do currently plug my amp directly into the wall. All my wall warts are gone. For my HT, add a 75” Sony TV, Marantz 7015 AVR & a Klipsch sub (although at zero volume the AVR & sub should not come into play).
I am considering buying the Furman IT-Reference 15i or 20i first as they are well reviewed & are priced very well on Amazon ($1,400 / $1,900). Before I pull the trigger, should I go dedicated power & at what amperage (my nephew, an EE & audiophile thinks I am drawing no more than 5 amps) as that will dictate the Furman model?
Interesting, my nephew thinks neither are worth the investment. His statement: “Do you have appliances on the circuit now? What kind of interference can they inject?...voltage drops would come from current draws...which trip breakers.
Not steady 60hz a good power supply handles. So it all comes back to was the power supply engineer dropped on his head as a child.”
”Personally I think it’s something audio people do when they have run out of gear to buy.”
Any thoughts or recommendations would be appreciated. Thanks!
@signaforce , I sent you a PM through the Agon message system. |
.
"which trip breakers." Motor loads can. Non motors loads no. .
I strongly disagree... I assume you are feeding your 2 channel audio equipment and H/T equipment from a single 15 amp convenience outlet branch circuit. FWIW per 2020 NEC (National Electrical Code), there is no limit on the number of 15 amp duplex receptacles that can be installed on a 15 amp convenience outlet branch circuit in a residential dwelling unit. Also worth noting ceiling light fixtures can also be connected to the same branch circuit wiring. Got LED lamps in them fixtures? Harmonic distortion noise... What wiring method did the residential electrician use to make up the in and out branch circuit joints/connections in the wall outlet boxes? Worst wiring method is using stab in the back residential grade 79 cent duplex receptacle outlets. That’s four connections, (2 hot conductors & 2 neutral conductors) for each outlet times how many wall outlets from the electrical panel to the wall outlet your equipment is plugged into. Problem with stab in the back outlets? Piss poor connections. Poor connections? AC high frequency harmonic distortion noise caused from micro arcing in all the stab in the back connections. I didn’t even mention the type of loads plugged into wall outlets on the same branch circuit. I looked at your equipment profile. I would recommend at least two 20 amp dedicated branch circuits. Maybe three... The big Sony TV with its Switch Mode Power supply isn’t helping the sound from the PS Audio BHK Signature Preamp and the Simaudio Moon 330A Amp. Those two analog and any other analog equipment should have it’s own 20 amp dedicated branch circuit. (Note 20 amp branch circuit.) Labor cost is the same whether 15A or 20A. Even the circuit breakers are the same price. Only difference is the price of the wire gauge used. Labor is the biggest cost. Labor for one circuits does not double for two, or triple for three... It doesn’t work that way. Material costs does though. . |
@signaforce said:
Sounds like you might be thinking all the breakers on the left side of the electrical panel are on one leg, and all the breakers on the right side of the panel are on the other leg. That is not the case... The breakers on each side alternate from Line 1 leg and Line 2 leg down both sides of the panel. The wider breakers, two breakers with a single common handle, are for 240V loads. Single breakers are for 120V loads. If the guy/gal that wired your house was a Licensed residential electrician he/she would not have put both furnaces on the same Line, leg. He would put one on Line 1 and the other on Line 2. By code he must attempt to balance known 120V loads on both legs the best as possible. Same for 20A branch circuits in the kitchen. Especially appliances. As for the two ACs (I assume 2 air conditioner outside condensing units), they should be 240Vac. They are fed from both legs. As for this:
The electrician has options that he will explain to you. The cheapest method is to install what is called a tandem breaker. This type of breaker is two single pole breakers in a common molded breaker case. It connects to one Line, leg bus in the panel. (Remove a single one pole breaker and replace it with a tandem.) It would take two tandem breakers to create two spare breakers. (The electrician can move existing 120V circuits around so all your audio equipment branch circuits are, or, are not fed from tandem breakers. (Note, best practices for multiple branch circuits feeding audio equipment, that are connected by wire interconnects, all branch circuits should be fed from the same Line, leg, in the panel. All from Line 1 or all from Line 2. NOT from both...) Example of a tandem breaker: Square D QO 2-20 Amp Single-Pole Tandem Circuit Breaker (Note the electrical panel must be approved for use of a tandem breaker. Most are unless it is really old. Your electrician will know. Breaker type approved are listed some where on the panel enclosure.) Second option is to add a small sub panel next, near, to the existing main electrical panel. Again the electrician will determine the best installation/wiring method for the sub panel location. If the main panel is exposed in a mechanical room in a basement cheapest sub panel install is next to the main electrical panel. Cheapest method is to install tandem breakers in the existing electrical panel.
|
@gdnrbob , thanks for the kind words. . |
Correct. Hot L1 leg to Hot L2 leg measures 240V, nominal. L1 to neutral as well as L2 to neutral measures 120V, nominal.
Correct. Both are fed from Line 1 (L1) bus, leg.
Example for illustration purposes only. Single phase 240/120Vac load center with 200A main breaker Note the turned out horizontal bus tie breaker connection tab that is part of the left and right vertical bus bars. Circuit breakers plug on to the bus bar tie tabs. The left vertical bus bar is Line 1 (L1) The right vertical bus bar is Line 2 (L2) Breakers Left side. ............. Breakers right side Top breaker L1 .............................L1 ................... L2 .............................L2 ................... L1 ............................ L1 ................... L2 ............................ L2 ................... L1 ............................ L1 ....................L2 ............................ L2 An so on to the bottom of the panel. No matter where a 2 pole breaker is plugged onto the breaker connection horizontal bus tie tabs the load side of the breaker is 240V nominal. Might be Top connection of breaker L1 and bottom connection L2. Or it could be top connection of breaker is L2 and bottom connection is L1. It just depends on where the 2 pole breakers are located in the panel. . |
There is a very good chance that digital front end equipment already has voltage regulators on the DC power side of the equipment. Good chance that holds true on at least solid state preamps. Maybe even for tube preamps. As for digital equipment the question is, does the equipment have filtering on the AC mains side that will filter out, prevent, digital hash from traveling back out on the power cord and re-interring on the power cords of an analog preamp and power amp that are plugged into a common power strip.? Even if the amp is plugged directly into the same wall outlet, same branch circuit, as the power strip. There was a well respected EE, his field was in electronics, that passed many years ago. He frequently posted on the AA forum. I remember he used to say the main reason, (paraphrasing what he said), for multiple dedicated branch circuits is to decouple the power supplies of digital equipment from analog equipment. That’s why I installed two dedicated 20A branch circuits. One for digital equipment, the other for analog. . |
@mitch2 said:
Probably fine. Loads are constant therein not fluctuating like with a power amp playing high dynamic music. Worth noting. When dealing with the available power from a wall outlet the amount of power available is not necessarily limited to the handle rating of the branch circuit breaker. Using a 15A circuit, #14 gauge wire, for example... Most people seem to think the breaker will trip when it senses 15 amps of current passing through it. That is a false assumption. UL / NEMA states the breaker must trip at a sustained current of 20.25A, (135% at less than one hour). (15A x 135% = 20.25 amps.) At 30 amperes (200 percent of wire rating) in less than 120 seconds. (15A x 200% = 30 amps). With quick fluctuating loads, at say 40 amps, the breaker may never trip at all if the load is only for a few hours or so. So the branch circuit breaker will continue to pass the connected load current well above 15 amps, 1800W for a short sustained duration or quick short fluctuations of current draw. Does VD, Voltage Drop, increase if the branch circuit wiring is #14 gauge and the connected load is over 15 amp? Yes, but how much VD depends on the length of the #14 gauge wire X 2. If the branch circuit wire is #12 gauge the VD is less. #10 gauge even less. I guess the point I am trying to make is, how well will a 15 amp, 1800W, rated power conditioner available power hold up to the availability power at the wall outlet branch circuit wiring fed from the electrical panel. (Electrical panel... A whole lot of available power.) The wall outlet will delivery well beyond 1800 watts for short intervals of current draw in time. What is the power head room, Service Factor, for short durations of overloading the power conditioner? Maybe 10%? 20%? Maybe 30%? I doubt it. . |
@mswale said:
I assume you mean the circuit breakers in an electrical panel. The breakers in the electrical panel are Thermal Magnetic Breakers. Per NEC, (National Electrical Code), only breakers Listed by the panel manufacturer can be used in the electrical panel. All branch circuit breakers used in electrical panels are Thermal Magnetic type breakers. You wouldn’t want just a magnetic type breaker. The thermal trip unit is for normal overloading of a circuit. It has a bi-metal strip that the circuit current flows through. When too much current passes through it the breaker trips open. (breaker trip curve). The magnetic unit in the breaker is for short circuit faults.The magnet trip part of the breaker is also what trips the breaker when there is high inrush current. (Good example is an old across the AC Line big power Krell power Amp). Here is a video of how it works. Note the panel shown is a Square D QO load center with a main breaker. The breaker used in the demonstration is an Eaton 15 amp breaker. Guys, don’t do this at home! . . FWIW. The video is of a regular type thermal magnetic breaker. Breakers found in new homes are still thermal magnetic breakers but also are AFCI, Arc Fault Circuit Interrupter, breakers. These are not cheap, They are expensive. Then there are GFCI, Ground Fault Circuit Interrupter, breakers. AFCI / GFCI Dual Function circuit breakers. They are really expensive! All these breakers also have a thermal magnetic trip mechanism built into them too. . |
@signaforce Said:
.
Problem... The Furman P 2400 AR has a NEMA 5-20P 20 amp plug. It will not plug into your 5-15R 15A wall outlet. Look at the photo of the P-2400 AR 20A Plug and the 20A receptacle required. Technically you will need a 20A branch circuit installed. The captive cord, I believe, was installed on the unit so it could get it safety test Listed. Listed like UL Listed or any other NRTL Listing. FYI, just guessing, (You know) you will never use a total of up to 15 amps of a combined continuous connected load. Continuous is defined 3 hours or more, NEC.
. |
@erik_squires said:
First, per NEC, all circuit breakers shall be Listed. Quote: NEC 110.3(B) Installation and Use. Equipment that is listed, labeled, or both shall be installed and used in accordance with any instructions included in the listing or labeling. End of quote. The section is talking about the manufacturer of the electrical panel. Not because a different manufacturer breaker is Listed. The different manufacturer’s breaker is not approved for use in the panel by the manufacturer of the panel. .
True, are any of them home inspectors retired licensed electrical inspectors or retired licensed electricians? The extent of their electrical knowledge is to use a plug-in circuit tester to check for an Open Ground at wall outlets. And GFCI outlets required in the house per Code. As for installing a different manufacturer’s circuit breaker in another’s manufacturers electrical panel that has been in the NEC for years. I know first hand, on a few instances the electrical inspector seen the violation. Not I ,well maybe I did, but usually the breaker was installed by a different electrical contractor/electrician previously. Problem is doing electrical work in old buildings in a city where a remodel is taking place. The General Contractor pulls a permit... All subs pull permits. The general contractor can’t call for an inspection until the subs call for an inspection, (if a sub’s work needs inspection before the general contractor’s inspection.) Problem for the Electrical contractor/Electrician? Usually at the final electrical inspection. The electrical inspector will say something like "did you add any new circuits?" LOL, he knows you did... "Show me the panel." Usually the circuit breaker manufacturer’s name is on the face of the breaker. Problem? The electrical panel manufacturer went out of business years ago. There are no NOS stock breakers. There definitely are not any Tandem breakers. They didn’t exist back then. . |
I think I would plug it into the analog. My reasoning is based on the linear power supply in the AVR. You can always try it both ways. Listen for differences. Look at the photo of the power transformer inside of the AVR. Power transformer is on the front left hand side. I believe that is a Bobbin type power transformer. It doesn’t look an like EI transformer to me. // Side note. When you receive the Furman P 2400 and plug everything into it make sure the plugged in equipment with power transformers, like power amplifiers, are powered off. Because of the VA rating size of the Toroidal isolation power transformer in the P 2400 the initial turn-on inrush current will be fairly high, then quickly fall off. You don’t want to add any loads on the P 2400 transformer to add any additional inrush current onto the 15 amp circuit breaker in the electrical panel, that may cause it trip open. (Unless the P 2400 has a soft start circuit built into it to limit power-on inrush current.) ??? The bigger the VA rating of a power transformer the better, when used to feed power amplifiers. . |
From the Furman P-2400 Owner’s Manual
WOW! . . An autotransformer does not provide isolation from the AC mains to the output side of the transformer. That is not the purpose, intention, of the design of the use of the eight tap toroidal "autoformer" in the P-2400. . |
I consider @erik_squires the Audiogon resident expert on Furman power conditioners. He has more knowledge than I on Furman power condioners technologically. @erik_squires is better qualified than I to answer your question regarding the design and circuitry of voltage regulation of the P-2400.
As for me the way the P-2400 voltage regulation, design, circuitry, is implemented sounds pretty sophisticated to me. Switching from a winding tap to another winding tap without causing a distortion in the sine wave or any type, no mater how fast, the switching method used is not an easy thing to do. Furmam seems to have it figured out without the user hearing anything from his audio system. If not you would be reading about it on the Net.
. |
Don't count on it! Verify 100% it is connected to the System Ground, Grounding Electrode System, of the electrical service equipment. Where does a CATV cable installer ground the grounding block if the cable point of attachment is on the other side of the House? I've seen where the installer stuck a stake in the earth and attached the ground block ground wire to the stake. . |
10 ft. captive 12/3 AWG,
@signaforce define gathered. I would not coil the the remaining 7ft in a neat tight small diameter coil. Imo, a small coil would act as an inductor. FYI do not cut off the cord to make it shorter. That more than likely would void the Furman 2400 warranty. Just a guess, I could be wrong, the length of 10ft cord may be for the proper operation of the type 3 point of use SPD, (Surge protection Device) inside the unit. With a type 3 SPD the minimum length of the branch circuit wiring from the electrical panel to the SPD matters. The minimum length is 30ft.
. |
@erik_squires said:
Not the breaker... The minimum AIR interrupting rating for a residential dwelling circuit breaker is 10KA. You will see it on the front of the breaker.
I agree... I just thought that’s why Furman made the 10ft cord captive to add more impedance in the minimum 30ft branch circuit wiring length. An added impedance current limiting fudge factor. (Just curious can the 2400 unit be ordered with a shorter cord. Say 5ft or 6ft?) I would check with the manufacturer first, before cutting the cord to make it shorter, to see if doing so voids the warranty. . |
Correction:
My bad. That should read: The minimum AIC interrupting rating for a residential dwelling circuit breaker is 10KA. You will see it on the front of the breaker. AIC, (Ampere Interrupting Capacity) rating. What the AIC of a 10KA circuit breaker means? The breaker contacts will open up to 10KA, 10,000 amps. (Don’t bet your life on it though.) / / / / . @erik_squires Said:
AIC corrected.. I know how MOVs work. .
BS. I told you the reason in my previous post. Think about... A Bolted Line to Line, or Line to EGC fault 1ft from a circuit breaker will trip open the breaker on short circuit protection. Sure in the heck don’t need 30ft. (Where’s your protection of the breaker) Think about it... Bolted... A heck of a lot more flow of amps than any MOV could possibly return to the source.
AIC corrected. I never said a Type 3 SPD had a AIC, Ampere Interrupting Capacity rating. jea48 said:
fault current rating, is not the same as, AIC, Ampere Interrupting Capacity rating. .
I seen the video. A $10.00 Type 3 SPD plug strip was used for the demonstration. . 2020 NEC 242.16 Type 3 SPDs
No mention of MOVs; No Exception, for Furman, Zerosurge, or Brickwall. . |
|
@erik_squires said:
LOL, "being less than cordial". LOL
@erik_squires said:
"It may help you to understand" I took that as an insult. .
The conversation is settled. You were wrong. You proved you were wrong when you introduced series mode SPDs into the conversation. @erik_squires said:
( should be AIC not AIR). in response to my post: 03-19-2025 at 03:43pm
(FYI, It was you that introduced AIR instead of AIC into the conversation. My bad for not catching it and correcting it at the time. Series mode SPDs blows your above statement out of the water. . Best regards, Jim . |