New electrical wiring specifications


I have installed a new electrical panel and am going to run 3 dedicated circuits to my audio wall. (40 feet).  2 monoblocks and other components Would like recommendations as to specifications for the electrician as to wire size and type, grounding, receptacles , etc etc etc.   thanks

digitaljoseph

Showing 3 responses by devinplombier

To live a happy life, electricity has to be understood and treated with respect. Just like your wife.

 

Especially the multi ground rod people you’re only supposed to have one ground rod per meter.

@raysmtb1 

Actually that’s not true. Code allows multiple supplementary rods as long as they’re connected to the main rod which is itself bonded to the panel. Rod-to-rod connections are prescribed by code.

What you cannot have is a ground rod that is not bonded to the panel. For instance, running a dedicated 20A circuit to one’s listening room, and that circuit’s ground is not returning to the panel; instead, it is connected to its own ground rod. That is expressly forbidden, not to mention it’s absolute sheer idiocy.