@hifidream said:
I was living in a loft apartment at the time in the end unit of five in a row. I don’t know if the building was grounded properly.
There is an unknown. A lot of variables. Age of the CATV coaxial cabling installation the biggest one.
I did not have the coax going though a surge protector which probably was the issue as you describe.
Not a surge protector. A grounding block. Two different animals entirely.
Example:
CATV coax cable shield Grounding Block![]()
As you can see its pretty basic. But when installed properly it gets the job done diverting a near by lightning surge to earth and most importantly to earth using the System Ground, Grounding Electrode System, of the electrical service of the building, dwelling unit.
The lower the grounding electrode to soil resistance the better for diverting the high voltage surge to Mother Earth. Simple OHMS LAW... (Grounding Electrode? Ground rod(s) connected together. UFER Ground, foundation footing Concrete Encased steel rebar + Ground Rod(s) tied together creating ONE Grounding Electrode.)
The only true way to know what the soil to grounding electrode resistance is, is to have it measured by a person that is qualified.
NEC requirement for the soil to electrode resistance is pretty much useless. IF tested the soil to electrode resistance requirement is 25 ohms or less. IF higher than 25 ohms, then an additional ground rod is required. No further testing is needed. NEC code is satisfied. That’s why electricians drive two ground rods. No testing needed. Therefore no test documentation is needed for the electrical inspector. A lot cheaper for the electrical contractor. Time is money...
( FWIW, IF tested the soil to ground rod may, for example, test 100 ohms. What are the odds driving a second 5/8" X 8ft rod will lower the resistance to 25 ohms or less?)
FWIW, IEEE recommends 5 ohms or less for a commercial electrical service’s grounding electrode.
.
The tech (30 year electrician and device repair man) was very clear, one path in for power and all connections or you risk creating a loop that encourages the lightening to travel around and exit after the damage is done.
First I doubt he is a licensed electrician. He is more than likely just an electronic repair service tech. He may be very good at what he does. He is entitled to his opinions...
Just a guess though for your experience at the time of losing audio equipment from a lightning event was more likely from poor grounding of the shield of the CATV coax cable. Just curious, was you using more than one branch circuit to feed your audio equipment at the time? Or all of the equipment was fed from one branch circuit?
Jim