westom,
LOL,
You just ramble on and on saying the same things over and over.
As for my posts on this thread I believe I answered all the OP’s questions and concerns accurately. Starting with SPDs and the importance of the integrity of the electrical service’s grounding electrode system/earth connection.
I would ask you to go back to the start of this thread and read my posts, but I know it would be a waste of time. It is obvious you have a problem understanding what you read.
Your understanding of NEC leaves a lot to the imagination.
I know you won’t, but you should at least take the time and read Article 90 of the NEC. It might help you better understand the rest of the book.
Pay close attention to the highlighted last sentence of 90.1 (A)
This Code is not intended as a design specification or an instruction manual for untrained persons.
Then read 90.1(B)
(B) Adequacy. This Code contains provisions that are considered necessary for safety. Compliance therewith and proper maintenance results in an installation that is essentially free from hazard but not necessary efficient, convenient, or adequate for good service or future expansion of electrical use.
Then read the Informational Note just below (B).
.
Through out this thread I said the NEC was bare minimum! I repeatedly spoke of the importance of the electrical service grounding electrode system/earth connection. I used IEEE recommendations, not NEC, for the minimum 5 ohm or less grounding electrode to earth resistance. I even said 2 ohms or less was better yet.
.