There is no issue with using either side of your panel or should I say both sides. As long as you bring in a separate neutral (white wire) with each hot. DO NOT BALANCE TWO HOTS ON ONE NEUTRAL IF BOTH HOTS ARE CONNECTED TO THE SAME BUSS IN YOUR PANEL. Did you notice I didn't say same phase?
A residential service is Single phase. Both 120volt lines in your panel are derived from a single transformer provided by your power company. (Thus single phase) There is no such thing as A-phase and B-phase in a residential panel. unless of course the house is huge and has a three phase service coming in. This would only apply to around 5% of the population.
If you are balancing two hots on one neutral they must be on opposing buses in your panel. Otherwise you could very easily overload the neutral and burn it up. This will cause an electrical fire in your walls long before you trip a breaker. This is not a grounding issue.
Anyway I hope I helped a little on this thread.
A residential service is Single phase. Both 120volt lines in your panel are derived from a single transformer provided by your power company. (Thus single phase) There is no such thing as A-phase and B-phase in a residential panel. unless of course the house is huge and has a three phase service coming in. This would only apply to around 5% of the population.
If you are balancing two hots on one neutral they must be on opposing buses in your panel. Otherwise you could very easily overload the neutral and burn it up. This will cause an electrical fire in your walls long before you trip a breaker. This is not a grounding issue.
Anyway I hope I helped a little on this thread.