toddverrone
If you’re in the U.S., it’s against code to install a second separate grounding rod. Also, having a second grounding rod can cause a voltage differential to develop between the two grounds, actually causing a current to flow on the ground wire.. all connections need to be clean, tight and tied into the same ground as the rest of the system.+1 about the grounding, and +1 about all connections being clean and tight. That applies to every connection in the service panel, including the breakers themselves, and the connections between your meter pan and the panel.