What wire to use instead of Romex


I want to install a dedicated 20amp outlet (likely an AQ NRG). The run from the main panel in the garage to my living room above is relatively short - maybe 25 or 30 feet. Because of HOA rules/regs, I cannot use Romex. Wires in the garage must be inside conduit. I will run 10AWG, but I'm unsure what other specs I should implement. Should I use solid core or stranded? Should it be copper? Is BX the way to go? I've read where using stranded silver or silver tungsten is best, but I'd be concerned about the silver oxidizing/tarnishing over time, especially at the junction points where the wire has no insulation. Is it important to twist the three (including ground) wires or will they perform just as well if run side-by-side? 

roccity

@jea48 

Best Practices:

It's recommended to use separate, appropriately sized 20 amp circuits with their own breakers and wiring to feed each half of the duplex receptacle. This ensures proper protection and avoids potential hazards.

Proper Method:

1. Separate Circuits:

Each 20 amp circuit should be run from its own 20 amp breaker in the electrical panel to its respective half of the duplex receptacle.

2. Appropriate Wiring:

Use 12 gauge Romex for both circuits, as it is rated for 20 amps.

3. Proper Termination:

Ensure the hot (black), neutral (white), and ground (bare or green) wires are correctly connected to their respective terminals on each half of the duplex receptacle. 
This is code ! 
 

Cheers 

@1971gto455ho 

It's recommended to use separate, appropriately sized 20 amp circuits with their own breakers and wiring to feed each half of the duplex receptacle.

I never thought about doing two runs to one duplex outlet. That's really kickin' it up a notch! I'm going to consider doing that. FYIW: My plan was to plug my stereo power amp directly into one outlet (manufacturer recommends NOT using any type of power conditioner) and my power conditioner into the other, which will have my preamp, DAC and streamer plugged into it.

@roccity  

Using appropriate wiring and breakers on a split duplex has been around for years and it is most definitely code and designed to be used that way as well. It is essentially no different than using a single outlet on a duplex box. Wiring must be done properly and you have absolutely no issues with safety. 
I did this because each one of my amps requires its own 20 amp breaker and I wanted to minimize dry wall and stud issues. The changes are well indicated in the panel and in the duplex box so any future people opening either will realize that multiple breakers have to be turned off. 
 Chreers

@1971gto455ho Said:

Best Practices:

It’s recommended to use separate, appropriately sized 20 amp circuits with their own breakers and wiring to feed each half of the duplex receptacle. This ensures proper protection and avoids potential hazards.

Proper Method:

1. Separate Circuits:

Each 20 amp circuit should be run from its own 20 amp breaker in the electrical panel to its respective half of the duplex receptacle.

2. Appropriate Wiring:

Use 12 gauge Romex for both circuits, as it is rated for 20 amps.

3. Proper Termination:

Ensure the hot (black), neutral (white), and ground (bare or green) wires are correctly connected to their respective terminals on each half of the duplex receptacle. 
This is code ! 

This is code ! 

No it is not. I posted word for word from the 2020 NEC code book.

I will look tomorrow for when NEC 210.7 Multiple Branch Circuits, the code edition year it was added to the NEC code book.  You may have wired your outlets the way you have them before 210.7 Multiple Branch Circuits was added to the NEC. 

Best practices is no guarantee that it follows or meets NEC or AHJ code. 

Your quoted material might be old. It should be updated to meet current NEC code. Or at least for the NEC code edition your state is still using. 

Please post the Website for the quoted material in your post. 

.

@jea48  

Do let me know for curiosity sake, it’s CSA approved here. I also run into many houses where 12 three was used in duplex boxes, that can get complicated and I personally don’t recommend it anymore, but it is legal. And I should add and don’t know that this would make a difference but the four wires and two duplex are in a double box.