Because of HOA rules/regs, I cannot use Romex. Wires in the garage must be inside conduit.
That also may be the AHJ (Authority having Jurisdiction) electrical code in your area as well. In Chicago IL only EMT conduit is allowed in residential housing. MC or AC/BX, nor flexible metal conduit is allowed. Going from memory in NY City, NY Romex is not allowed.
You need to contact the Electrical Contractor you will be using. He will know what you can use. Also have a copy of the HOA requirement for him to read.
As for using EMT conduit I would suggest you ask the Electrician to twist the Hot and Neutral conductors together before pulling them in the conduit. Pull the EGC, (Equipment Grounding Conductor) along side the twisted pair when installing the branch circuit wiring in the EMT conduit. The EGC could be #12awg green insulated solid copper wire if you use #10awg copper wire.(FWIW, the electrician may tell you you don’t need an EGC insulated conductor in the conduit. Per NEC the EMT conduit is an approved EGC. It’s your call... I would have him install the EGC insulated conductor anyway.
Solid core wire only for the Hot and neutral conductors. Tell the electrician you want solid wire not stranded. He is going to resist the suggestion. Hold firm.
.
The run from the main panel in the garage to my living room above is relatively short - maybe 25 or 30 feet.
Did you guesstimate Up, over, across, and down?
.