VA vs. Watts? How much power do I need? Power cond


Hello,

My prologue amp says it has 300 watts power consumption. And my NAIM cd player says 12VA. How do they add up(watts and VA)? I am trying to figure out the max power I need to select the correct power conditioner.

i am so hopeless with these tech subjects:)
128x128parkcaka
Not into a reactive or capacitive load, only into a purely resistive load, does VA=watts.
The measurement of electrical power that is computed by multiplying volts times amps. In a DC circuit, volt-amps (VA) and watts are the same because DC circuits do not add inductance and capacitance that take away power. In AC devices, volt-amps ratings are higher than watts. For example, in an uninterruptible power supply (UPS), the volt-amps rating is approximately 60% higher than the actual wattage.
Some power conditioners are rated in WATTS (PS Audio, Hydra, eg) and some are rated in VA (Equitech, eg).

To size a power conditioner rated in VA: add up all the equipment power ratings that are given in WATTS and double that value. Add the (2xwatts) to the total power rating of equipment given in VA. That's the size of the power conditioner in VA. Or in your case, 2x300+12=612VA. Pick the next size larger than 612 to be sure.

To size a power conditioner rated in WATTS: add up all the equipment power ratings that are given in WATTS. Add the watts to the total power rating of equipment given in VA. That's the size of the power conditioner in WATTS. Or, 300+12=312 Watts. A 300W unit will do it.

Also note that amps can have a power output greater than their nominal rating. Check the owners manual and see what's the maximum power draw/rating that the amp has. For example, if your amp is 300W into 8 ohms and 400 Watts into 4 ohms, then use 400 watts.

Best-bet-can-never-go-wrong: size your power conditioner for the wall power standard of 15 amps/120volt or 1800VA.