Power conditioning for multiple dedicated circuits


I have been looking through the discussions and cannot find specifics on how people condition a dedicated circuit. I ran 4 new lines to my music room. There are two wall receptacles where I removed the tab on each to have each outlet on the duplex a dedicated circuit. I have my amp, preamp and phono stage plugged into 3 and a monster power center plugged into the 4th to cover all other items(subwoofer, DAC, streamer, turntable power supply).

All the conditioners I am finding are similar in design to my Monster where there are 8+ outlets. Are there any single outlet models for my application or would I need to allow space to stack up multiple units only utilizing one from each?
dhite71

Showing 8 responses by jea48

I ran 4 new lines to my music room. There are two wall receptacles where I removed the tab on each to have each outlet on the duplex a dedicated circuit. I have my amp, preamp and phono stage plugged into 3 and a monster power center plugged into the 4th to cover all other items(subwoofer, DAC, streamer, turntable power supply).

I ran 4 new lines to my music room.
As in four individual lines that do not share a common conduit or cable.
Example: Four 2 conductor with ground Romex cables?
Or two 3 conductor with ground Romex cables?

There are two wall receptacles where I removed the tab on each to have each outlet on the duplex a dedicated circuit.
Why did you pick that wiring method?

There are two wall receptacles where I removed the tab
’Tab’ as in only 1 tab per duplex receptacle outlet removed? The tab on the Hot contact side? Neutral side not removed. If yes, then you fed each duplex with a 3 wire 120/240V multiwire branch circuit? Two hot conductors, one shared neutral conductor, and one EGC (Equipment Grounding Conductor).
If yes, you do not have four 120V dedicated circuits. You have four separate 120V circuits. I would not recommend this wiring method for feeding audio equipment. Especially when the equipment will be connected together by wire interconnects.

.
I'm not suggesting power conditioners don't work- in fact, they may work effectively in eliminating more than what you intended.
True

Most of the ac mains "dirty power" found in our houses is caused by devices, equipment, and appliances, found in the home. Including the audio equipment itself.

As for dirty power put back out on the ac mains by the audio equipment, that is why more than one dedicated  branch circuit is used.  
YMMV.  
builder3454 posts  

08-08-2021  
 12:46pm  

I think you’ve now protected your 12 wire circuits with a 40A breaker, which is a huge mistake.
Correct. The breaker needs to be a 2 pole 20 amp breaker.
dhite71 OP147 posts

08-08-2021
12:23pm                         


@jea48

I did the 2nd scenario you described. I chose this because when I went to Lowes to pick up the Romex they had a bundle of 12/3 wire that was 1/2 price due to a return. Therefore each duplex receptacle has 2 hot, 1 neutral and 1 ground. I removed the hot wire’s tab and wired to a double pole 40amp breaker so they each have their shared 20amp breaker but you cannot forget to switch one side off in the event of later work. I did not research nor ask about this method so the only reason was simplicity. What are the disadvantages? I originally thought about using 10ga wire but got swayed by the wire on sale. From your response I suppose sharing the ground and neutral disqualifies them from being dedicated. What is the disadvantage for they way I have them wired?

I did the 2nd scenario you described. I chose this because when I went to Lowes to pick up the Romex they had a bundle of 12/3 wire that was 1/2 price due to a return.
It’s nuts what Romex is selling for now. You can buy 12/2 and 12/3 MC (Metal Clad) aluminum armor cable cheaper than Romex. Supply and demand!

Before I explain where, imo, you went wrong in the type of wiring and wiring methods you used please explain why you are looking at buying plug in power conditioners? Are trying correct something? Are you hearing something from the speakers of your system you don’t like? Did you hear it before you added the 4 new circuits?

.
dhite71 OP149 posts

08-08-2021
6:23pm

I have been thinking more about my 12/3 wire configured for two separate circuits. There is a single neutral and ground wire going back to the panel.

Does this matter when all neutral and ground wires in a house are going back to their same respective bus bar? The neutral and ground bus bars are even connected within the panel.

I would like to understand how two of each returning the panel compare to a single run.

@ dhite71 OP ,

You said in an earlier post you did not hear any differences in the before and after installing the 4 new circuits. As a rule that is not what what audiophiles say. Usually they say their system sounded better and well worth the cost of having a dedicated circuit(s) installed.
And then sometimes there will be a post saying that multiple branch circuits caused hum and buzzing from their audio system. Usually the latter is caused from the wrong type of wiring was used and or the wrong wiring installation  method(s) was used.


As a rule if the connected load is not all that big, therein say less than 20 amps, it is recommended all dedicated circuits be fed from the same Line, (L), leg, from the electrical panel for audio and or video equipment that is connected together by unbalanced wire interconnects.

(Jmho, it also depends on the design of the audio equipment power supply and how the designer connected the B- and signal ground to the metal chassis of the equipment.
The quality of the power transformer used in the equipment can make a big difference. How well does it control capacitance coupling from the primary winding to the secondary winding(s).

//

In most cases the total combined audio equipment ac mains 120V power load is 10 amps continuous or less. The reason given for installing more than one dedicated branch circuit is to decouple the power supplies of the equipment from one another. Especially digital equipment from analog. Something else may be to keep a SMPS(s) away from non SMPS equipment power supplies. With just one branch circuit with everything just plugged into a common power strip there is not any decoupling.
(FWIW, some power conditioners install filtering to isolate receptacle outlets from one another).


With the 3 wire 120/240V multiwire branch circuit, (MWBC), only the unbalanced load, current, of the two 120v circuits to neutral loads return on the shared neutral conductor back to the source. Example, if there is 4 amps on one circuit to shared neutral and 2 amps on the other circuit to shared neutral only 2 amps will return on the neutral conductor to the source. The balanced 120V L1 to neutral and 120V L2 to neutral loads are in series with one another. The two balanced loads are being fed by 240V. (120V respectively measured across each plug/receptacle outlet) That means any digital hash fed back out on the ac Line of the power supply of digital equipment, that is fed from one ac Line, will be in series with a preamp or power amp that is fed from the other ac Line.


Here is a video for you to watch. The guy does a pretty good job of explaining how the secondary winding of a single phase split winding transformer works. (Same way the Utility Power Transformer that feeds your house works).
Look at the wiring on the split phase secondary winding of the transformer as being a 3 wire 120/240V MWBC. Light bulbs represent your audio equipment.
https://www.youtube.com/watch?v=eVamt9IdQd8

//

Even two individual installed 120V dedicated branch circuits that are connected to breakers on opposite Lines, legs, can cause noise problems when unbalanced wire interconnects are used to connect equipment together.
(One branch circuit connected to a single pole breaker on L1 and the other branch circuit connected to a single pole breaker on L2).


Here is an old quote from a White Paper by ExactPower. (The Web Link is no longer any good.

"Less than 300 microamps of ground loop current can cause hum as it flows in an unbalanced audio interconnect cable. However, harmonics of 60Hz that are generated from lighting dimmers or switch-mode power supplies sound like Buzzz mixed with a bit of Hummm and are more easily coupled by even smaller currents. Harmonics can add together when equipment is powered from different phases, so clearly there is an advantage to specifying same-phase electrical service to power the electronics systems in most cases....

Any leakage currents on the safety ground wires of split single phase load circuits fed by different phase legs will add together due to the 240V potential difference....

Power conditioners do not solve any of these common problems: Cross phase coupling (doubles hums & buzzes) .... What actually does solve them: Same phase power.

http://www.exactpower.com/elite/assets/pdfs/theTRUTH.pdf


"Any leakage currents on the safety ground wires of split single phase load circuits fed by different phase legs will add together due to the 240V potential difference.... "


240V potential difference? Voltage measured from one receptacle Hot contact to the other receptacle Hot contact, of each split wired duplex receptacle, fed by a 3 wire 120/240V MWBC.


Jmho this is at play as well.

(Jmho, it also depends on the design of the audio equipment power supply and how the designer connected the B- and signal ground to the metal chassis of the equipment.
The quality of the power transformer used in the equipment can make a big difference. How well does it control capacitance coupling from the primary winding to the secondary winding(s).

.
I would be remiss if I did not mention if an Electrical Contractor/Electrician was hired to install four 120V branch circuits he/she would not install MWBC (s). The reason is the NEC requires all new 15A and 20A branch circuits supplying outlets, per 210.12 (A), shall be AFCI protected. The problem with using a MWBC the 2 pole breaker will nuisance trip for no apparent reason because of the shared neutral.

Example of a 2 pole 15A or 20A AFCI breaker:
https://www.homedepot.com/p/Square-D-QO-20-Amp-2-Pole-Combination-Arc-Fault-Circuit-Breaker-QO220CAF...


NEC (National Electrical Code)

210.12 Arc-Fault Circuit Interrupter Protection.
Arc-fault circuit-interrupter protection shall be provided as required in 210.12 (A), (B), (C), and (D).


(A) Dwelling Units. All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed in dwelling unit kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas, or similar rooms or areas shall be protected by any of the means described in 210.12(A)(1) through (6).

.
To add to my last post. If a duplex receptacle is split and the two receptacles will each be fed by a separate branch circuit NEC 210.7 shall apply. (It doesn’t matter if one is fed from L1 and the other from L2 or both circuits are fed from two breakers that are fed from the same Line (L), leg.


210.7 Multiple Branch Circuits. Where two or more branch circuits supply devices or equipment on the same yoke or mounting strap, a means to simultaneously disconnect the ungrounded supply conductors shall be provided at the point at which the branch circuits originate.

.
danvignau911 posts

08-13-2021
7:02am

I hope you ran all four outlets to the same leg on your electrical panel. If not, do it. You will be pleasantly surprised, and all it takes is to switch the breaker around. It is not even necessary to remove any wires. Just pop them out and re-arrange them.
@ danvignau

The OP installed two 120/240V 3 wire MWBC (Multiwire Branch Circuits).
Each MWBC has 2 hot conductors and 1 shared neutral conductor. With a shared neutral the two hot conductors cannot be fed from the same leg. Doing so would double the current, amps, on the neutral conductor.

The OP therefore must fed each hot conductor of each MWBC from both legs.

Only the unbalanced load of the MWBC returns on the shared neutral conductor to source. The balanced 120V load of L1 to neutral and L2 to neutral are in series with one another and are being fed by 240V. The remaining unbalanced load returns on the neutral conductor to the source.
https://www.youtube.com/watch?v=eVamt9IdQd8