Power conditioner wire gauge? Serious issue


So I just figured out that all the 10 gauge wiring I have may be a problem if the power conditioner I use only uses 14 or 16 gauge wires to connect all those outlets you plug into in the back of those devices.

The specs are not part of the description when you buy Power conditioners.  Everybody recommends a dedicated 10 gauge wire from the panel but fails to consider what power conditioners use. 
 

Is this a serious problem? 

 

jumia

Showing 1 response by sls141

IMO this is not a "serious problem" at all. (Assuming you're using a 20 amp breaker to feed the 10 gauge wire.)

Look at it this way. The circuit using 10 gauge wire feeding the outlet is "overbuilt." The power conditioner is not "underbuilt" due to what is feeding it.