EDIT to my above post.
For some reason #4 Web link no longer works
Here is the Link. (Turn down your volume first.)
.
New electrical wiring specifications
I have installed a new electrical panel and am going to run 3 dedicated circuits to my audio wall. (40 feet). 2 monoblocks and other components Would like recommendations as to specifications for the electrician as to wire size and type, grounding, receptacles , etc etc etc. thanks
@skyy92677 said:
New house.
Was it your idea to add an additional ground rod to the two that are already there? Adding the additional ground rod wouldn’t have solved your problem. It may have given you a lower soil resistance for the grounding electrode system for the Earth connection of the electrical service. The main purpose for the connection to Earth is for lightning protection. .
What did the Master Electrician say about the two quotes above problem? I can not visualize any way the Siemens Type 2 SPD could cause such an event as you have described. The electrical panel should be full of 120V single pole 15 and 20 amp AFCI, (Arc Fault Circuit Interrupter), branch circuit outlet breakers. An AFCI breaker has a built-in micro processor that senses a series or parallel arcing fault event. I would think the Siemens SPD would drive the electronics in the AFCI breakers nuts, causing them to trip open on a false arc fault event. FWIW, my understanding, for one of the reasons for NEC requiring surge protection at the main electrical equipment panel, was to help protect the AFCI breaker’s internal electronics from high voltage transient surges. If you have the breaker turned off the electronics in the AFCI breakers are not protected. You said the house was just recently built. I don’t know about your State but my State requires the builder to stand behind any defects, I believe for one year. I suggest you call the builder and tell him you have a serious electrical problem. Ask him if he will have the Electrical Contractor send out a troubleshooting Service Electrician to look at and fix the problem. Before addressing the hum/buzzing issues with your audio system zero in on the Siemens SPD at the electrical panel and the toaster buzzing, (when being used), when the SPD breaker is closed, (connecting the SPD to the electrical bus) of the panel. Then you can tell the electrician the problem with your audio system. Not that it should matter, I assume the toaster uses a 2 wire cord and plug. No safety equipment ground is used. Just curious, does any of the Links provided below sound like the buzzing sound you are hearing? CAUTION, turn down the volume before listening to the examples. Especially the last example. This is a standard 60Hz ground loop hum. 1) 60Hz hum Or maybe this. 3) 120Hz Or maybe this. 4) 120Hz buzz (Make sure volume is turned down first) . 120Hz could indicate a high level of harmonic distortion on the AC mains. You said you tuned off all the breakers in the panel at one point. Including the Siemens SPD breaker. Only having one breaker on that fed your audio system. Doing so didn’t make any difference. Hum was still present. But not as loud when the Siemens SPD breaker was turned on. I still am shaking my head on that one. Makes no sense what so ever... That’s the first thing the Service Electrician will want you to show him. I would want to see and hear that first hand using the toaster.
How about any neighbors that are fed from the same Utility Power Transformer as your house. Any solar panels on the roof(s)? Are any of the neighbors experiencing electrical problems like you are having? . |
@ditusa Said:
I agree on the use of MC (Metal Clad) armored cable. I’m just not a fan of the galvanized steel armored MC cable. I personally would use aluminum armored MC cable. From my listening experience, as well from that of other audiophiles, galvanized ferrous magnetic steel can add grain as well slightly restrict the openness, air, of the musical presentation.
The highlighted text is of the greatest importance. Though NM sheathed cable, (Romex), is good and widely used, I think 2 wire with insulated ground MC cable is better. (Solid copper wire.)
To all that may be reading this post, MC armored cable. NOT AC / BX armored cable. Make sure the Electrician buys and installs MC cable. Example of MC cable: (For purposes of showing the three insulated conductors are twisted together. I am NOT recommending the manufacturer.) 2 conductor with insulated ground MC armored cable Note the photo shows solid copper conductors. Ad is for stranded. For audio branch circuit wiring solid copper conductors is recommended. Southwire is a very good cable manufacturer FYI, though Anti Short bushings are not required by NEC code for MC cable, I highly recommend you tell the electrician you want them installed anyway. If if he says you don’t need them. Tell him, you want them anyway. They are cheap and it will take the electrician about 15 seconds to install one. . *** AC / BX Armored Cable *** Make 100% sure the electrician installs MC and not AC / BX armored cable. Big difference between the two. Southwire Armorlite 125-ft 10 / 2 Solid Aluminum BX/AC Armored Cable Look closely at the picture of the section of the cable. Note the two insulated copper Line conductors and the bare 16awg aluminum safety equipment grounding/bonding conductor.
"An armor assembly (combination of the interlocked armor & bonding strip) that is recognized as an equipment grounding/bonding conductor per NEC 250.118(8)." You don’t want this... . |
@dhite71 said:
That’s not what Fremer has now. https://forum.audiogon.com/discussions/dedicated-power-circuits Read my post on 02-23-2023 at 04:06pm I see five 120V branch circuits connected to circuit breakers installed on the same Leg, Line, in the Sub Panel. Read my comments I posted for Fremer’s sub panel. (Note: The the wiring on the left side of the bottom of the panel. I’m not sure but I think there is a Type 2 SPD, (Surge Protection Device), mounted to the bottom of the panel.)
. |