Measurements for a dedicated line


The question of whether a homeowner should get a dedicated line is often like "should I get bangs." It’s a little complicated. Here are a couple of reasons to consider not:

I. My experience is that you won’t eliminate all the other noise coming from your home even if you do run a dedicated line. I still hear motors switching on and off despite being on completely different circuits.

II. A little resistance and a little inductance may actually be a good thing in keeping noise out of your line, so overkill on the wire gauge may not help this.

Why you definitely should get a dedicated line, with thicker wiring:

 

Less voltage sag.

 

Voltage sag means that under load the resistance in the line will cause the AC cabling int he wall itself to consume some of the AC voltage, giving your gear less volts to work with. This sag is proportional to current, so the more amps your gear is drawing the more sag.

This sag is something you can measure. There are two things you need to look: The hot to neutral voltage and the neutral to ground.

With nothing on the circuit your N-E (neutral to earth or ground) should be 2V or less. If it’s significantly higher than that stop and call an electrician. That’s true for any circuit in your home. High N-E values are indicators of a problem which may be in the circuit or in the service wiring from outside to the panel.

What happens when you turn your equipment on and play music is that the line will sag. The H-N (hot to neutral) voltage will drop, and the N-E will go up. Some sag as you turn on big amps is normal. So long as you are not tripping breakers you are fine. What you want to measure is the sag after your system has stabilized and while it’s playing music.

Keep an eye on the N-E value, as this will be a good indicator of the sag independent of the incoming line voltage. It may also point out where you may have issues. That is, if you measure an extra 2V of N-E, your sag is probably around 4V, so you went from 120V to 116V and you can be relatively comfortable it isn’t outside influences.

Of course, any good multimeter will work for this but I like plug in meters with built in N-E measurements. This one is cheap, and the N-E may not be hyper accurate, but it is the only device I’ve found on Amazon that will show you both the H-N and N-E voltages at the same time.

The nice thing about any plug-in type voltage meter is you can watch it over  a couple of days without hand holding probes in the socket.

If you find another which does both please post.

 

 

erik_squires

So, A'gon apparently got upset with me that I said A M A Z O N in an e-mail.  Sheesh! :D

Post removed 

Are you sure you have an Equipment Grounding Conductor at the outlet?

100% most definitely; on both outlets being discussed. I can take my multimeter and read 121.6 volts across the hot and neutral (no load), and the exact same voltage is measured across hot and the EGC.

Maybe I’m not understanding you correctly, but I’m failing to comprehend why you think there should be some voltage on the EGC for these outlets (under load)? I was always under the impression that the EGC was to keep your equipment as close as possible to ground potential, and provide a safe path for ground-fault current to flow. My thinking is that if there was any voltage on the EGC, and I had in place a GFCI outlet; it would trip.

The voltage drop / 2 method only works if the voltage drop is equal.  It is possible the voltage drop is higher on the hot due to resistance. 

Best to measure with a multimeter for the most accurate results.

Post removed