My system was hit by lightening, it traveled through the coax cable line into my video processor via HDMI and then hit my projector. I had everything on quality surge protectors but it didn’t matter. The electrician I took the equipment to for insurance purposes said that lightening likes to have a path in and out so having things plugged into different wall outlets is an issue.
The electrician I took the equipment to for insurance purposes said that lightening likes to have a path in and out
I’m pretty sure he meant more than one earth connection to the electrical grounding system of the house. (From mother earth to the inside of the house and back out of the house to mother earth.)
All mother earth connections should be connected to the main electrical service equipment, service entrance neutral conductor that is bonded to the metal enclosure of the electrical service equipment. That especially includes the shield of the CATV providers coax cable.
On the outside of your house just before where the coax cable enter your house there should be a grounding block. (sometimes the block is mounted in a plastic weather proof/resistant enclosure).
Here is where it can get tricky. How close is the grounding block from the outdoors electric meter socket enclosure? More than 20 feet?
If 20ft or less a minimum #14awg copper ground wire, (I would use #12awg solid copper minimum), install from the ground block lug to the grounding electrode conductor that come outdoors from the main electrical service equipment and connects to a ground rod(s) in the earth. (Some times the electrical service equipment is mounted outdoors beside the electric meter socket enclosure).
Use an electrical split bolt to connect the #12awg solid copper wire to the #6 bare solid copper wire, (#6awg solid bare copper is the minimum size per code). (I prefer #4awg bare solid copper wire).
Clean the bare #6 copper ground wire with a piece of emery cloth or fine sand paper.
Example of a split bolt.
If distance from the grounding block to the grounding electrode conductor is greater than 20FT post back for instructions.
Grounding and Bonding of Communications Systems
.