Lifting the ground is a bad idea. What you need to do is isolate your system from the house. This can either be achieved by using a isolation transformer like a Plitrom Medical Grade Type 1 or by using a balanced transformer (60/60) (BPT, Equi-Tech, etc). In either case make sure you purchase a transformer that not only handles the max load of your system but also has a little extra because all transformers convert energy to heat. So to make sure dynamics are not restricted I would look at a transformer 25% to 50% larger than your system needs.
Regards,
Alan Maher