Electrical Panel Grounding


Beyond electrical code requirements, why does the sub panel earth ground, with its own earth ground, need to be tied to the main electrical panel ground?
wgutz

Showing 1 response by cleeds

All grounds must be bonded together at the service panel. This is for safety reasons, and to ensure that breakers will trip properly under fault.