He has installed Isolators near the receptacles, which is a big ON/OFF switch (which has and earth line), this will then run into the US style duplex outlets (115v 20amp)...see link below...a check with Furutech, say's that 230v 20 amps running through is not a problem...
this will then run into the US style duplex outlets (115v 20amp)...see link below...a check with Furutech, say's that 230v 20 amps running through is not a problem.
If I understand you correctly, Furutech told you that you could use a US NEMA 5-20R receptacle for 230V is that correct? Maybe in Singapore but not in the US.
The NEMA 5-20R can only be used on a nominal 120V 20 amp branch circuit. Never to be used on 230V, connected to a 20 or 32 amp breaker.
Maximum power that can be connected to a NEMA 5-20R receptacle:
120V X 20 amps = 2400va (residential family dwelling unit). 1920va commercial/industrial applications.
Here is what you will have if you follow what Furutech has proposed,
230V X 20 amps = 4600va. Granted the power amp would never normally draw that much power. But what if??
another example,
230V connected to a 32 amp breaker. 230V X 32A = 7360va
I notice from the picture of the amp it has an IEC male connector for a detachable power cord. Why not just buy a cord that will fit the configuration of a 230V 32 amp, or higher, rated receptacle for Singapore?