I did some resarch on the Malaysian electrical system. It is the same as United Kingdom. North America also has incoming live and neutral from the power company, and the electrician installs the grounding electrode. The same grounding rules apply in both cases. The power company transformer (the power source) is grounded at its location.
For circuit breakers to trip when there is a ground fault, the current has to be able to get back to the source (i.e, the power company transformer) at a rate that is high enough to cause the breaker to trip. The resistance of the earth is too high to accomplish this. The breaker will just "see" the ground fault current as a normal (high resistance) load and not trip. That is why any supplementary ground rods must be bonded to the main grounding electrode (which is also connected to the incoming neutral, which is also grounded at the source (transformer). I'm glad that you understood what I was trying to say.
For circuit breakers to trip when there is a ground fault, the current has to be able to get back to the source (i.e, the power company transformer) at a rate that is high enough to cause the breaker to trip. The resistance of the earth is too high to accomplish this. The breaker will just "see" the ground fault current as a normal (high resistance) load and not trip. That is why any supplementary ground rods must be bonded to the main grounding electrode (which is also connected to the incoming neutral, which is also grounded at the source (transformer). I'm glad that you understood what I was trying to say.