Are you saying the dedicated lines are only grounded to the pipe in your backyard ? This is dangerous for two reasons. First, such a setup is highly prone to a lighting strike. Second, should a fault develop in the wiring, the circuit breakers will not trip.
In order for a circuit breaker to trip when a fault is present, there has to be a ground path from the branch circuit, all the way back to the utility company transformer.
When a supplementary grounding electrode (which is what you have) is installed, it has to be bonded to the previously existing grounding electrode. It also sounds like the new ground rod you installed is too far away from the pre-existing ground rod.
Branch circuit ground wire should be the same gauge as the current-carrying conductors. What country are you in ? In America we speak American Wire Gauge (AWG - #8, #10, #12, #14, etc.) not millimeters.