I did watch him install the wire and did notice when he went to hook up the wires to the panels he seemed to remove a lot of the yellow sheilding to allow for the copper ground to be hooked up.
The outer yellow jacket is not a shield. It is just an outer PVC jacket to house the three conductor and help protect the the insulated conductors from physical damage.
I wanted a dedicated line in hopes for a better signal and noticed that when I turn the ceiling fan on with the remote I hear a small poping sound from my speakers???
If you are 100% sure the fan never caused that problem before call the electrician back out......
Possibilities?
While the electrician was in the panel he may have disturbed, moved, some wires where they terminate on the neutral buss as well as the branch circuit breakers.
Solid wire that is not curled around a terminal screw and then secured by a tightened down the screw, (in most cases the wire is straight and the terminal tightened down on the straight wire). In the latter case movement of the wire can cause the connection to become lose sometimes.
Another thing that can happen in the case of plug in breakers, such as Square D QO breakers, a breaker/s may not be fully seated on the buss connecting tie.
One of the above examples could be the case with the branch circuit that feeds the ceiling fan.....
If a connection is loose the connection can series arc under a start up load condition and settled down when the load drops off.
Or you just never noticed the problem before.
At any rate call the electrician and explain the problem you are experiencing.
I am sure he will come back out and check and re tighten all the wire terminations in the panel.
He will also check to make sure all branch circuit breakers are plugged onto the buss connecting ties all the way.