Dedicated circuit


I read a lot of posts on the subject, but my question is I have 6ga feeding a subpanel . My 220 compressor and other circuits are fed from the subpanel.
Should I run my dedicated circuit off the main or would it be ok to pull from the subpanel?
If I run from main it will be close to 100ft of wire, so would be best to use 6ga.
Or, off the subpanel which would be about 40ft, then I would use 10ga from subpanel to dedicated outlet.
Any opinions?
Thanks
128x128skids

Showing 1 response by whart

I’m not @jea48, but until he chimes in, I can tell you that I run a compressor as part of my hi-fi system-- fairly substantial, at one point a 1 hp 13 gallon unit- but even with smaller units, there was a nasty electrical snap that could be heard through the system when the thing cycled. The way I resolved that at the time was to run it from a 240 line with a step down transformer.
When I moved, I had more flexibility and installed a dedicated line just for the compressor that went nowhere near the subsystem feeding the hi-fi. The hi-fi has it’s own iso tranformer (10kVa- a beast) that runs to a sub panel that feeds 10 gauge Romex to the outlets. The compressor is not coming off that big iso transformer but comes from the main panel for the house and has a smaller iso transformer as a buffer.
You are probably creating a little bit of racket in a hot rod shop, but it’s worth checking to see how much noise you hear through the system when things are quiet. That "snap" was quite pronounced for listening purposes in a quiet, dedicated room. Dunno if that helps. Love to hear about the hot rods though!