Thanks for all the advice.
I am still leaning toward 15 kva Isol trans due to the size of my system. I have a dedicated 100 amp service from the electric company transformer feeding a dedicated 9 circuit/ 80 amp isoclean breaker panel. This service shares the same power meter with 2 other 100 amp services feeding my 2 household breaker panels.
I have 3 systems fed by the isoclean breaker panel which includes hometheater with projector, processor, large multichannel amp, 3 powered subs, multiple sources, housewide music distribution with 1 large multichannel amp and 1 large stereo amp and multiple sources, and finally 2 channel system with 1 amp, 4 powered subs, digital, vinyl, reel to reel sources, main preamp and phono preamp. Also several large plasma screens.
In the future I anticipate more computer based sources and processors, more amplifiers and more screens and possibly a 4th system.
during the summer and fall I usually have 2 systems working simultaneously. Winter and spring usually 1 system at a time. On rare occasions all 3 are going.
All electric services come in through my garage which is the location of my isoclean breaker panel. The 450lb ultra k will be installed in the garage immediately adjacent to the panel. This location is completely isolated physically from all systems.
I am still leaning toward 15 kva Isol trans due to the size of my system. I have a dedicated 100 amp service from the electric company transformer feeding a dedicated 9 circuit/ 80 amp isoclean breaker panel. This service shares the same power meter with 2 other 100 amp services feeding my 2 household breaker panels.
I have 3 systems fed by the isoclean breaker panel which includes hometheater with projector, processor, large multichannel amp, 3 powered subs, multiple sources, housewide music distribution with 1 large multichannel amp and 1 large stereo amp and multiple sources, and finally 2 channel system with 1 amp, 4 powered subs, digital, vinyl, reel to reel sources, main preamp and phono preamp. Also several large plasma screens.
In the future I anticipate more computer based sources and processors, more amplifiers and more screens and possibly a 4th system.
during the summer and fall I usually have 2 systems working simultaneously. Winter and spring usually 1 system at a time. On rare occasions all 3 are going.
All electric services come in through my garage which is the location of my isoclean breaker panel. The 450lb ultra k will be installed in the garage immediately adjacent to the panel. This location is completely isolated physically from all systems.