One measure of a surge protector is the clamping voltage. That is, at what voltage does the surge protector actually start to work. Whole house surge protectors are limited to no less than ~ 600 Volts (instantaneous) between a leg and neutral or ground. That’s up to 1,200V if symmetrical.

The best surge protecting strips and conditioners clamp below 200 Volts.

Please keep this in mind when deciding whether or not to use surge protectors at your PC, stereo, TV, etc. in addition to a whole house unit.

I wrote more about this here:

 

https://inatinear.blogspot.com/2021/09/time-for-new-surge-suppression.html

No manufacturer of whole house surge protection claims that their devices alone are enough for sensitive electronics when you check the fine print.

erik_squires

Showing 1 response by jea48

If you talk to the folks at ZeroSurge, they will tell you that you need point of use rather than whole house because most surges are emanating from inside the house.

It’s true most high voltage transient surges are created by induction motor load appliances and or equipment found in the home.

Branch circuit wiring in the home is fed from an electrical panel. If an appliance or a piece of equipment sends a high voltage transients surge back on the branch circuit wiring what better place to suppress, clamp, it than at the electrical panel with a Type 2 SPD.

Second line of protection is the Type 3 plug-in point of use SPD (Surge Protection Device). (Type 3 SPDs should not be connected to branch circuit wiring less than 30ft in length fed from the main electrical service panel.)

FYI, SPDs should be, approved, certified, Listed, UL 1449 3rd edition.

Eaton’s guide to surge suppression

Leviton SPD / NEC 2023 code.