Whole House Surge Absorber.


I just installed myself "whole house" surge protector. I've already lost garage door opener due to line spikes last winter. Siemens style panel protector takes space of two standard circuit breakers - dual circuit breaker with built in MOV type surge arresters. Taking two spaces in my panel allows to suppress voltage spikes between each phase to ground and between two phases. Installation was very simple - placing double breaker in place of two singles and connecting thick ground wire to ground bar. Two green LEDs show active protection. Siemens recommends using it as additional protection when expensive electronic equipment is involved. I have all my gear plugged into Furman Elite 20PFI conditioner that has very tight non-sacrificial surge protection. My gear (DAC+Class D amp) is powered 24/7 but I always unplug it during thunderstorms. How do you protect your gear?
128x128kijanki

Showing 1 response by jea48

Kijanki,

For the best possible protection the SPD (Surge Protection Device) should be installed in 2 spaces nearest the main breaker or in the case of a main lug only panel the SPD unit should be installed in 2 spaces nearest the panel feed wires that connect to the electrical panel.

It is very important that your main electrical service grounding electrode system is installed and wired correctly. All connections should be mechanically tight and connections are not corroded. Going from memory, IEEE/ANSI recommends a 5 ohm or less soil resistance for a proper/good earth grounding electrode system. Your SPD is only as good as the grounding electrode system resistivity/conductivity connection to mother earth.

Make 100% sure any/all CATV, TV antenna, satellite dish, and phone incoming cables/lines that enter your home from outside are properly grounded, connected, to the main grounding electrode system of the main electrical service of your home. This is a must when dealing with a near by lightning strike.
Jim