Surge Suppression vrs. Lighting and Power Spikes
Check out the video on lightning, a little down the page. >http://science.howstuffworks.com/nature/natural-disasters/lightning.htm . |
Problem with grounding is that it has to be done (to be legal and insured) with at least gauge 10 wire to ground rod with bends of no smaller radius than 6".Kijanki, You are correct on the size of the wire. #10 awg copper or #8 AWG AL minimum. NEC 2008 (810.21 (H)) I would never use AL..... The way I read it if a separate earth grounding electrode is used the grounding electrode, ground rod, shall be connected to the main electrical service grounding electrode system with a bonding jumper no smaller than #6 awg copper or equivalent. (NEC 2008 810.21 (J)) The important thing here is the antenna grounding conductor ends up being connected to the main grounding electrode of the electrical service of the premises, end result..... Is that the way you understand it? . |
I would bet most residential earth grounding electrodes are inadequate when it comes to lightning protection. If memory serves me right the maximum electrode to earth resistance of 5 ohms per IEEE. http://www.cpccorp.com/deep.htm http://www.erico.com/public/library/fep/LT0359_1.pdf . |