If you want some EFI/RMI protection on the feeder to the sub panel,use type AC cable.The conductors are twisted and protected by a metal or aluminum covering.The aluminum covering is much lighter than the metal.You can get this AC cable up to #2AWG.They also make a version of it with 2 grounding conductors,if you need isolated grounds.When putting any type of cable (romex,cords,) in any type of conduit,instead of individual conductors (THHN THWN) you will need conduit about 3 to 4 times larger than required for individual conductors.Its because of heat.You need lots of air space around cables because a cable is already tightly covered with a jacket.This is a example of it.Size of conduit for 3 #10 copper conductors,half inch.Size of coduit for 10/2 romex,2 inches
Sub Panel hook up Question??
This may have been answered but- I just ordered the Equitech 10Q subpanel-Does it matter if you hook it up next to your main panel and then run long runs of 10 guage romex or am I better off hooking it up in the closet in my stereo room and use shorter runs of 10 guage?? thanks,gary
3 responses Add your response