The average home theater / stereo is going to need 1-2 dedicated circuits. These are usually 12 gauge with 20 amp outlets.
One each dedicated circuit, you can install several receptacles for equipment.
Each circuit run with Romex will have it's own dedicated ground and dedicated neutral as part of the Romex. Sharing neutrals / grounds is really not compliant with modern NEC...
If the power is wired correctly, there is no need for 7 dedicated circuits, 10 gauge wire...30 amp breakers...
This is all over the cliff, I mean seriously.
Are you listening to a stereo?...or...
are you arc welding?
One each dedicated circuit, you can install several receptacles for equipment.
Each circuit run with Romex will have it's own dedicated ground and dedicated neutral as part of the Romex. Sharing neutrals / grounds is really not compliant with modern NEC...
If the power is wired correctly, there is no need for 7 dedicated circuits, 10 gauge wire...30 amp breakers...
This is all over the cliff, I mean seriously.
Are you listening to a stereo?...or...
are you arc welding?