Transformers don't really care whether they are getting 60 or 80 or 100 Hz. Now if you were talking 100,000 Hz, that is a different story, but 10s of Hz doesn't matter. The electronics downstream don't care either because they only see DC voltage coming off the rectifiers. All that changes is the ripple frequency, which if your power supply is properly designed, will be so low in level that nothing will notice. So no, there shouldn't be any problem.
As for motor control - now that can be a problem. Depends on the type of motor, but in some cases, changing the line frequency will change the motor speed...
Arthur
As for motor control - now that can be a problem. Depends on the type of motor, but in some cases, changing the line frequency will change the motor speed...