New dedicated lines have high noise floor.


I just installed two dedicated lines for my system.  Each is on its own 20a circuit breaker.  I used 10 gauge hospital grade MC cable (exact same length) and Cardas 4181 duplex outlets.  I was expecting a quieter noise floor and better sound.  I have a 3x to 4x increase in the noise floor compared with a regular outlet nearby.  One of the circuits has a "crackling" sound.  For the best results, I need to put my amp and source equipment on a single outlet.  If I use both the sound gets worse.  Any ideas?  I need to have my electricians come back, but would like to have some audiophile wisdom for support.
pg62

Showing 2 responses by jea48

@ pg62

Why did you use hospital grade MC cable?
For audio 10-2 with ground would have been better.


Problem with hospital grade MC cable there are 4 wires. one Hot, one neutral, and two equipment grounding conductors. The geometry of the way the 2 equipment grounding conductors are installed in relationship to the current carrying hot and neutral conductor makes it more possible that a voltage is induced onto the equipment grounding conductors.

Did the electrician terminate both circuits on circuit breakers on the same Line, leg, in the electrical panel? Both on Line 1 or both on Line 2?

One of the circuits has a "crackling" sound.
That sounds like a loose connection. Could be a faulty circuit breaker, or a poor connection between the breaker to the connecting bus tie in the electrical panel.What type/manufacturer panel is it?
.

@ pg62

AC Power Wiring Types (cont’d) Metal Clad (MC)is manufactured in both steel and aluminum with twisted conductors that help reduce AC magnetic fields. Although the steel jacket helps reduce AC magnetic fields, the twisting of conductors has the greatest effect on reducing these fields. Another benefit is the constant symmetry of the phase conductors with respect to the grounding conductor which greatly reduces voltage induction on the grounding wire. (NEC article:330)


Two conductor plus 1 ground MC (Metal Clad)is a good choice for Non-Isolated Ground A/V systems. MC cable contains a safety grounding conductor (wire). The three conductors in the MC cable (Line, Neutral and Ground) are uniformly twisted, reducing both induced voltages on the ground wire and radiated AC magnetic fields. The NEC article 250.118 (10)a prohibits the use of this cable for isolated ground circuits because the metal jacket is not considered a grounding conductor, and it is not rated for fault current.


Two Conductor plus 2 ground MC (Metal Clad)may be used in an Isolated Ground installation, because the cable contains two grounding conductors (one for safety ground and one for isolated ground). The conductors are twisted, but the average proximity of the hot conductor and the neutral conductor with respect to the isolated grounding conductor is not equal. Under load, this will induce a voltage along the length of the isolated ground wire, partially defeating the intent of isolation (see Ground Voltage Induction section of this paper).

~


Single-Phase 120/240V electrical service is most commonly found in residences and smaller commercial buildings, and is commonly used to feed AV equipment. One key advantage that single phase has over three phase is that while harmonic currents are still present, only even order harmonics can add in the shared neutral, and they are uncommon, since the waveform would be asymmetrical. In addition, use of single-phase 120/240V can result in at least a 6dB reduction in noise floor as compared to three phase if the capacitances of the connected equipment are relatively well balanced. Furthermore, if a signal cable is connecting two pieces of ungrounded equipment powered from opposite phases, the leakage current flowing in it will increase (causing more noise) as compared to powering the equipment from the same phase.

Integrating Electronic Equipment and Power into ... - Middle Atlantic


Read pages 31 thru 35