@ pg62
Why did you use hospital grade MC cable?
For audio 10-2 with ground would have been better.
Problem with hospital grade MC cable there are 4 wires. one Hot, one neutral, and two equipment grounding conductors. The geometry of the way the 2 equipment grounding conductors are installed in relationship to the current carrying hot and neutral conductor makes it more possible that a voltage is induced onto the equipment grounding conductors.
Did the electrician terminate both circuits on circuit breakers on the same Line, leg, in the electrical panel? Both on Line 1 or both on Line 2?
.
Why did you use hospital grade MC cable?
For audio 10-2 with ground would have been better.
Problem with hospital grade MC cable there are 4 wires. one Hot, one neutral, and two equipment grounding conductors. The geometry of the way the 2 equipment grounding conductors are installed in relationship to the current carrying hot and neutral conductor makes it more possible that a voltage is induced onto the equipment grounding conductors.
Did the electrician terminate both circuits on circuit breakers on the same Line, leg, in the electrical panel? Both on Line 1 or both on Line 2?
One of the circuits has a "crackling" sound.That sounds like a loose connection. Could be a faulty circuit breaker, or a poor connection between the breaker to the connecting bus tie in the electrical panel.What type/manufacturer panel is it?
.