Here's today's developments....
1) 3/3 to Square D QO type subpanel.
2) 12 dedicated runs to all the outlets (plastic gang boxes)
3) To each outlet the black will be hot, the white, neutral and the red returned back to the subpanel and all the red wires put onto an isolated ground bar. This bar will be grounded to the outside and a grounding rod buried deep.
4)Since plastic outlet boxes will be used the bare copper wire in the 10/3 will not be used and tied off.
5)Now I can use normal hospital grade receptacles and not IG type. All because the isolated ground bar (holding the red wires from all the outlets) will have its own ground to outside and separate from the main panel.
Note: The red wire will be green taped and and grounded at the subpanel.
Thanks to all of you guys.