Installing an AC Grounding System, Need Advice


Later this week, my electician will begin work on my electric project, which will involve the installation of a 7.5kVA isolation transformer that will be fed from a separate meter tap. The isolation transformer will be installed in front of a new dedicated circuit panel that will house the dedicated circuits that will feed my listening room. All the dedicated circuits will be fed from the same side of the bar in the new panel in order to maintain consistent phase.

As Sean has advised in a separate thread, I know it is important that I check - and upgrade as necessary - the ground for my AC system. (My house was built in the late 1950s, and, from the looks of things, not much has been done since that time to upgrade the electric service. So I am nearly certain that I will find the grounding system leaves much to be desired.) I also know from discussion in various other threads that it is important for the entire electrical system in my house to share a common ground. So I expect that I will need to upgrade the grounding system into my main circuit panel and then tie the isolation transformer and the new dedicated panel back to that same grounding system.

The work on my house is being performed by a qualified electrician, but, as I have noted in other threads, I would like advice on the audiophile details that can make a difference in the sound (in this case, the noise floor) of my system. Perhaps I should also mention that my plan involves installing a separate dedicated circuit for each of my seven components. Given that this sort of a set-up is more prone to ground loops, I am interested in advice regarding how to avoid them with this set-up.

With that as background, would any of the resident experts be willing to share with me the details of how to install a high quality grounding system for my AC power? I would appreciate as much detail as possible regarding the materials to use as well as installation advice.

I have read some advice in other threads recommending two separate copper grounding rods driven into the ground relatively close to each other with a weather-proofed connection between the two rods that is, in turn connected to the electrical system. I have also seen some advice that I believe involves wiring one of these connected ground rods to the main house circuit panel and the other connected ground rod to the audio portion of the system (i.e., in my case, the isolation transformer and the new dedicated circuit panel). Please let me know if this is headed in the right direction and, if so, please help me to fill in some details (dimensions of the copper, advice on how to drive it into the ground without mangling it, distance between the redundant rods, any other details you see fit).

As always, thanks for your help and patience.
cincy_bob
Post removed 
Post removed 
Jea48, the "water method" that you commented about is the method that was used by my electrician to drive the rod. The power was disconnected and the ground wire hadn't been connected to the rod yet. My electrician works for the one of the biggest electrical contractors in town. Are you saying that what he did wasn't legal? I've heard others use this method in my area as well.
If you have trouble driving the ground rods into the soil, my electrician used an electric impact hammer, and it worked well.
Post removed 
I'd check out www.equitech.com. They're the people into balanced power; however, they also have different articles that can be downloaded via computer. One of these articles is "setting up an a/c ground." I used one 10' 5/8" copper ground rod. If you use two, they need to be separated by at least 8'. As for putting the ground rod into the ground... Use water. Slowly dribble it into the hole that the rod is making, as you plunge it up and down. The pressure of the rod tip--(like a high heel shoe-pressure per square inch, ouch!), and the water at the hole's developing surface will cut through the dirt in no time. Be careful with that project. I've read multiple grounds can be dangerous. Hope all this helps. Good Listening!
Shasta, about a month ago, I hired a registered electrical engineer to develop drawings for the modifications to my residential electrical system. What I have been doing in this forum is educating myself so that I can raise the right topics with - and ask the right questions of - my electrical engineer and my electrician.

The service drawings for my system do not contain any detailed specifications for the grounding of the new circuit panel. Without the aid of this forum, I would not have known that there was any alternative to simply grounding the new panel back to the incoming water line that currently serves as the grounding electride for my electric system. And, without any discussion of the topic with my electrician, I am sure he would have opted for this single ground without any discussion and without me being aware of any alternative for a secondary ground. The education Jea48 has provided me regarding the option of installing a secondary outside new earth ground electrode allows me to have an intelligent conversation with my electric professionals that I could not otherwise have even initiated.

Jea48, thanks very much for all the information you have shared. It is very helpful to me and will significantly enhance my ability to communicate with my electrical engineer and electrician.
Cincy: You really can't do a free, engineering project via an audio Forum. That's a bit much to expect, both financially and even more importantly, from a liability standpoint. You are very bright, curious, and well spoken, but, respectfully, and I'll buy the first beer - y'all are drifting into a real project. And, respectfully, if we don't know that ground rods come in 10 ft lengths, and that driving one takes a specialized tool, and is the ultimate in apprentice physical labor, and that there are a ton of NEC requirements to be met, well...

Saying that you may want to consider engaging a freelance (not an engineering company) registered electrical engineer to prepare several drawings on what you wish to do. You can verbalize your electrican through it, but, that is always poor practice. That includes an as-build of your entire home system. Expensive, but hand waving a Journeyman electrican will burn up a stupid amount of hours; and here in N. CA, the billing rate will be about $80/hour.

Not a shareholder, employee, sales rep of any mentioned product. The XIT system is a large, hollow ground rod packed w/ trick material. It is vented at the top to absorb ambient humidity, thusly maintaing a very low impedance with the contacting soil throughout the year despite weather conditions. It is used by Honeywell for their DCS (Distributed Control Systems) in their localized Remote Instrument Enclosures handling plant control of digital inputs/outputs and analog signals in the milliamp level. It is installed in at least one Chevron refinery in California.

It also is, possibly, stupid overkill for a residential app., but in this day and age when 6loons is reviewing new-car priced transports/DAC's, I'm lost...

If your curent system is in good condition, and has a measured reasonable impedance, I wouldn't loose sleep on this...
Post removed 
Jea48, thanks for all your input. It is really valuable to me as I lack personal expertise in this area. Here are some answers to your questions:

1. Soil and Moisture - As my user name implies, I live in the Cincinnati, Ohio area. Our soil in this area involves a lot of clay. We tend to have normal midwestern weather with a fair amount of precipitation yearound but occasional droughts in the summer months. Let me know if additional information would be helpful in this area.

2. Isolation Transformer - My isolation transfomer is an MGE Topaz isolation transformer that is described in the following web link:

MGE Topaz 100 Installation and User Manual

This web link will lauch a pdf file that contains the full user manual for my isolation transformer. The specifications for the unit are contained on page 11 of the document. My unit is model no. T-100H-7500. It is a hardwired 7.5kVA transformer (see pg. 12 for the specifications of the various model numbers).

The unit provides 140dB of common mode noise attenuation and 65dB of normal mode noise attenuation. I believe the transformer also provides the electrostatic shielding that you mentioned in your latest post.

By the way, my use of the word, "taps," simply shows my inexperience with the subject matter. I had no technical basis for the use of that term.

Based on the advice in your latest post, it sounds like I should use the transformer to step down the 240V primary voltage to 120V at the output stage.

It would be a lot of help to me if you would explain a bit more to me about the primary and secondary grounding electrodes in my system. If I understand your posts to date, you are suggesting that, to comply with code and safety standards, the grounding electrode on the primary stage of the isolation transformer must be tied back to the grounding system at my main electric panel in my house (i.e., the clamp that is attached to my water pipe service where the service enters my house).

When you refer to the secondary grounding electrode, are you referring to a second ground connection from the secondary side of the isolation transformer? Did I understand your first post in this thread to suggest that it is best to have a ground for this secondary side of the transformer that is independent of the water pipe ground that is used as the primary ground for my electric system? I have seen a lot of cautionary advice about the use of two separate grounds within an electric system. The cautionary advice seems to say that it is never acceptable to have two separate grounding systems for two parts of an electrical system. Can you clarify this part for me?
Post removed 
Post removed 
The Lyncole system can be laid vertically or horizontally. They make kits for either. Lyncole is a US based company and uses high quality part than some of the other systems manufactured in China or other places.
This system will is probably one of the best grounding systems out there at this time.
Cincy_bob,
Also check Atitec electrolytic ground rods, (www.atitec.com), which are similar to Lincole but may be priced more competitively. It is worth talking to either company before installing this type of grounding - if you're going this far, it's worth understanding the soil content at your place, and the number of rods that are optimal for adequate grounding. The rod is not driven, the hole does need to be backfilled with electrolytic compost to provide adequate soil contact.
Shasta, I have done a little bit of research on the XIT grounding system that you suggested. It looks like a very serious product designed primarily for commercial and industrial use. Can you provide any further information on the practicalities - or "how to" - of using this product in a residential application? Do you have a ballpark estimate of what the 10-foot grounding system might cost, and what the incremental installation cost might be? Does this system require specialized installation skills beyond those of an ordinary electrician whose experience consists of more conventional grounding systems?

I would also be interested in a bit more education on your comment that "BTW, you'll never drive a rod yourself..." Is there specialized equipment involved in the installation of a ground rod? Does the process typically involve driving the rod into the ground (visions of driving a railroad spike)? Or, alternatively, does the proces involve boring a hole in the ground, placing the rod in the hole, and backfilling the hole? (Based on my limited reading on the XIT system, it seems that it is installed in the latter manner.)

Any further information you can offer would be much appreciated.
.
Jea48 and Shasta, thanks for your responses.

Jea48: The input to the isolation transformer will be 220V on the primary side. The transformer offers different taps to allow either 220V output or a stepped down 110V output on the secondary side. My electrician was planning to feed the new dedicated panel with the full 220V of output from the secondary side of the transformer. If this configuration does not make sense given my desire to run all the circuits from only one side of the bar, I would be interested in your observations and advice.

Regarding the water service in my house, it is metallic (copper) water service. I can see that there is a ground clamp on my water service ahead of the meter where the service enters my house. I believe that ground wire is tied into the ground for my AC service on the other side of the house. (I have not traced the wire in order to verify this; however, the ground wire runs in that general direction before it disappears above some non-removable ceiling tiles, so it is a safe bet.) I think I remember seeing a ground rod driven into the ground outside my house in the near vicinity of my electric service that I assume is also tied back to my main electric panel

Shasta: My house is not under construction. On the contrary, it was constructed in the late 1950s. As mentioned above, I believe my electric system is using a ground rod that is driven into the ground in the near vicinity of my electric service. Either I or my electrician will need to fish around in the ivy outside my house to verify the existence and location of that ground rod.
Shasta: From what i can tell ( i am NOT an electrician and don't understand all of your terminology ), your post seems to advocate a redundant ground system for the AV system that ties back into the main ground system. Is this correct? If not, could you either explain what XIT ground rod system is or provide us with a link that shows pictures / offers an explanation?

Other than that, your ideas of shutting down the AC for several hours and cleaning all of the existing contacts is a great idea. As i've posted before, the lack of continuity in a connection, especially to ground, can result in poorer performance than expected. Sean
>
Sigh, stand back for a rush of unsafe, uniformed advice; starting off with 2 separate ground rods. There's only one way to do a grounding system (is this a house under construction?) and that's at least NEC minimum, and even that can be improved on. Any cock-eyed deviations from that will induce laughter from your electrician and scowls from the inspector.

Do a real, Code-defined, isolated ground install for *each receptacle. Any Journeyman electrician should understand this.

Install a Lyncole XIT ground rod system. Watch your electrical contractor's eyes bug out as they start to call you Sir and Mister. If this is an existing house, leave the current rod in place, and use the XIT as an adjunct. Scrub, clean, and retighten all exsisting connections on the existing rod. BTW, you'll never drive a rod yourself...

If an exist. house, call the utility and get a 4 hour disconnect. Clean and retorque the incoming lines at the service panel. Then, clean and retorque everything on the load side of the main breaker.

*I* would have done metallic conduit; but the twisted wiring is certainly a nice feature. That's why they make vanilla and chocolate...

Obssesive was actually a left-hand complement-- *grin*. When I bought my condo several years ago, I replaced all switches and receptacles w/ Leviton 20A Spec grade devices. Wire ends were cleaned, everything backwired clamped, and I purchased an Armstrong torquing screwdriver for finalizing the connections; required per NEC 110.3(b).

Recap: Torque all connections, new or old. Isolated ground for every receptacle. XIT ground rod. Have the impedance checked on the grounding electrode conductor, and shoot for *way under the NEC 25 ohms number; which the XIT should deliver.

Strike the set, it's a wrap.