How to remove ground pin on power cable


This is a power cable being used for my subwoofer. I have a ground loop currently. According to the manufacturer of my subwoofer, due to it's design, it is perfectly safe to remove the ground. Right now I do so with a cheater plug but I would like to avoid having to use it. The power cable in question is Oyaide Black Mamba V2

How easy is it to take a power cable apart and disconnect the ground? Is it best to do so at the IEC side or the pronged side? What is the process for doing this?

Thanks
nemesis1218

Showing 1 response by heaudio123

UL943 governs GFCI in the US, with Mexico/Canada having similar specs, and I believe EN specs are similar.

- 2003 update to improve surge suppression to protect components.
- 2006 updated to detect some miswiring
- 2015 added automated testing and a whole host of required fault detection w.r.t. the proper operation of the circuit. Newer GFCI should be much safer than old ones w.r.t. guaranteed operation.  Self check is once every 90 minutes.


GFCI outlets have more stringent requirements on what happens when a fault it detected compared to GFCI breakers, but most new breakers on the market appear to be adapted the more rigid requirement to disconnect power, not just indicate a failure.

Was looking at some of the controller chips and they will even detect ground/neutral faults, and will check for failures more often.