I did the same type of installation. From the main panel, I installed a 2-pole 100-amp breaker. From this breaker, a run of 1-inch EMT feeder to a 100-amp main-lug sub panel (check with your codes if your sub panel requires a main breaker). The feeder consists of two #3 phase wires, a #3 neutral and a #8 ground. The two phase wires were twisted to minimize common mode noise.
The 100-amp subpanel has a ground bar kit installed. From the sub panel 20-amp breakers, I ran one 10/3 wire to each outlet. The hot/neutral wiring to the outlet was conventional but the green ground wire was attached to the outlet ground screw. The outlet itself was isolated from the box by a plastic strip. (I used BX and metal boxes so I wanted to isolate the BX sheathe from the ground path.)
The nuetral wire from the outlet went to the neutral bar of the sub panel and the ground wire went to the ground bar. The grounds and neutrals are on their own bar - conventionally the G and N's would both go on the neutral bar.
The neutral bar in the subpanel is directly attached to the feeder neutral and the subpanel ground bar is directly attached to the feeder ground conductor - NOT to the bonding fittings. Back at the main panel, the feeder G and N are attached to the neutral bar (no ground bar there - old panel) but it does not matter because the "star" node of the ground is in the subpanel.
Again, check with codes. But my setup has not given me any headaches or hums.
The 100-amp subpanel has a ground bar kit installed. From the sub panel 20-amp breakers, I ran one 10/3 wire to each outlet. The hot/neutral wiring to the outlet was conventional but the green ground wire was attached to the outlet ground screw. The outlet itself was isolated from the box by a plastic strip. (I used BX and metal boxes so I wanted to isolate the BX sheathe from the ground path.)
The nuetral wire from the outlet went to the neutral bar of the sub panel and the ground wire went to the ground bar. The grounds and neutrals are on their own bar - conventionally the G and N's would both go on the neutral bar.
The neutral bar in the subpanel is directly attached to the feeder neutral and the subpanel ground bar is directly attached to the feeder ground conductor - NOT to the bonding fittings. Back at the main panel, the feeder G and N are attached to the neutral bar (no ground bar there - old panel) but it does not matter because the "star" node of the ground is in the subpanel.
Again, check with codes. But my setup has not given me any headaches or hums.