Lissnr,
You did not mention how far from the house the garage is.
Distance from the house main electrical panel, to the new audio room sub panel? You may need to take into account voltage drop.
You stated the new sub panel feeder will be buried 18" below grade.
Direct burial cable or PVC conduit with single conductors?
I would recommend PVC conduit over direct burial.
Copper or aluminum feeder conductors?
Copper will cost you an arm and a leg.....
And I hope you are not thinking of an isolated dedicated equipment ground rod.
The equipment grounding conductor shall occupy the same raceway or cable as the feeder conductors and shall terminate in the same panel as the feeder conductors, NEC.
First off you do not need a main in the sub panel, that is unless your local code requires it. If your local code does not require a main then all you need is a main lug only panel.
The sub panel and sub panel feeder will be protected by the breaker at the main electrical panel for the new feeder.
As for the sub panel what brand are you looking at?
I would use a panel with copper bus. If you have the money I would go with a Square D NQOB panel board. The bus is copper and the breakers are bolt on.
Curious, did the electrician say he could?
You did not mention how far from the house the garage is.
Distance from the house main electrical panel, to the new audio room sub panel? You may need to take into account voltage drop.
You stated the new sub panel feeder will be buried 18" below grade.
Direct burial cable or PVC conduit with single conductors?
I would recommend PVC conduit over direct burial.
Copper or aluminum feeder conductors?
Copper will cost you an arm and a leg.....
And I hope you are not thinking of an isolated dedicated equipment ground rod.
The equipment grounding conductor shall occupy the same raceway or cable as the feeder conductors and shall terminate in the same panel as the feeder conductors, NEC.
I'm expecting the main breaker on the house side of it to probably only be 100 amps? as well as the main breaker on the sub panel to only be 100 amps too... mostly because
First off you do not need a main in the sub panel, that is unless your local code requires it. If your local code does not require a main then all you need is a main lug only panel.
The sub panel and sub panel feeder will be protected by the breaker at the main electrical panel for the new feeder.
As for the sub panel what brand are you looking at?
I would use a panel with copper bus. If you have the money I would go with a Square D NQOB panel board. The bus is copper and the breakers are bolt on.
I'm expecting the main breaker on the house side of it to probably only be 100 amps? as well as the main breaker on the sub panel to only be 100 amps too... mostly because the 100 amp breaker is 1/3 the $300 cost of the 125 and I can't imagine I'd be drawing that much current all at one time?I do not believe you could install a 125 amp breaker in the main 200 amp electrical panel anyway. It might fit but the panel is not approved for that large of a breaker.
Curious, did the electrician say he could?