What concern did the engineer express? The way you describe is legal except for patient care areas where the two ground paths must be separate. (Maybe that's his thinking).
Your chances for a ground loop are not from the two ground paths but from plugging in separates into different outlets. If you have an amp on one outlet, a preamp in another, a DAC in another and a transport in another still, each component has four separate ground paths when the interconnects are installed. Any unbalance in the neutrals may induce a ground loop hum, especially if the grounding conductors back to the panel are of different lengths.
Your chances for a ground loop are not from the two ground paths but from plugging in separates into different outlets. If you have an amp on one outlet, a preamp in another, a DAC in another and a transport in another still, each component has four separate ground paths when the interconnects are installed. Any unbalance in the neutrals may induce a ground loop hum, especially if the grounding conductors back to the panel are of different lengths.