Electrical Panel Grounding


Beyond electrical code requirements, why does the sub panel earth ground, with its own earth ground, need to be tied to the main electrical panel ground?
wgutz

Showing 1 response by gs5556

Is the sub panel in the same building as the main panel or is it in an unattached garage?

What do you mean "with its own earth ground"? You cannot -- in the same building -- run a separate grounding conductor from a sub panel to a location other than where the house service is grounded. If there is a grounding conductor from a sub panel to, say, a water pipe that is more than 5 feet where the water pipe enters the house, the house water piping could be energized in the event of a fault. 

The sub panel must have a ground bar that is bonded to the sub panel and the circuit grounds get attached to the bar. That ground bar must be bonded to the main service panel ground at the point of entry by either a separate wire or metallic conduit to the sub panel from the main panel.

The sub panel must have an isolated neutral bus that prevents the sub panel circuit neutrals from being grounded upstream of the service panel, resulting in neutral currents raising the potential on the sub panel metallic parts and ground.

If the sub panel is in an unattached building and fed from a breaker in the main panel, then the sub panel needs its own earth ground (to a ground rod) and does not need a grounding conductor to the main panel.