Dedicated power,long power cords - waste of time?


I am thinking about putting in a couple of dedicated lines but if I do this I will require extra long power cords, say about 20 feet in length, as the dedicated outlets must be installed across the room from where my system resides? There is no way around this.

Currently I have 3 pieces on 1 15 amp line. Bryston amp, Hovland preamp and my digital gear is plugged into a small BPT conditioner also on the same line. Installing 2 lines would allow me to drive the preamp and amp on their own lines and leave the digital alone on its own.

The downside is having to run 2 really long power cords which I would plug directly into the amp and preamp's IEC inlets.

Am I spinning my wheels here? Is this money down a rathole???

All opinions and/or related personal experiences are most welcome.
rgd

Showing 1 response by alrau1

Driver has the right idea, but the wrong product; what is needed is a product that goes by the tradename "Wiremold" or its equivalent. It's a form of wall-surface-mounted, decent-looking, paintable metallic conduit that will meet NEC requirements. The hollowed-out molding will not meet NEC req's. Wiremold sells pre-formed inner and outer corners, surface-mount outlet boxes and other useful accessories for successful completion of your "impossible" job.

BTW, I would have the electrician use STEEL (not aluminum) BX armored cable up to the point where you make the transition to the Wiremold because of its superior magnetic shielding properties.