Dedicated power


After a lot of research and consideration, mostly between power conditioners and dedicated circuitry, I have decided to go with 3 dedicated lines. One for amp one for pre and a 3rd for CD or digital. What I'm thinking is that I can pull the wire myself and then hire a professional electrician to do the breaker work and wall terminations using hospital grade outlets. My question is what wire should I use? I have heard of people using 12-2 or 10-2 but don't have knowledge of wire specific details. Anybody up on this?
markus1299

Showing 1 response by gs5556

Most, if not all, new receptacles have terminals that accomodate 14, 12 and 10 wire. Even the 15-amp 5-15R. The limiting factor is not the wire but the circuit breaker. The breaker must not pass more current than the wire ampacity that's it's connected to. So you could put a set of 500MCM wires on a 20-amp breaker feeding a 15-amp receptacle (that's not physically possible, I'm making a point). In your case, #10 wires are good for 30-amps but when used for a branch receptacle circuit, the breaker can only be 20-amps max. When the breaker limits the current, a larger wire size is not an issue. Correct wire sizes are equivalent to steel beam sizes - you can go bigger than what's needed to do the job if you don't care about money.

Where and why #10 instead of #12 when a 20-amp breaker is the most permitted? When voltage drop is a concern. Generally, #10 is used when there is a 50 foot or more total wire length from panel to receptacle. Less than that, you are wasting money as #12 is more than adequate.

Also keep in mind that any 115 volt device with a UL label can be safely be put on a 15-amp circuit. That's where the confusion lies over 15-amp receptacle with 20-amp breakers. The circuit will never draw the 20-amps as you are limited by code to size your system based on a ten receptacle maximum on a circuit, each one 180 VA, or 1,800 VA (15-amps) total.

Overheating a circuit is an end-user created problem (power strips and extension cords). It's your choice for the wire sizes, #10 will work and fit properly.