Dedicated Lines


I have a question about the optimal way to run a dedicated line. I currently have 3 dedicated circuits for my 2 channel equipment. One thing I noticed after the installation is that they all travel though the same metal conduit to the breaker box. I wonder how "dedicated" they really are if they are in the same conduit. Also, I do not remember what guage and brand of wire was used for the run. What is the "best"? The run is fairly short (30ft would be a guess). Lastly, they all go to a subpanel that has very few things on it (runs the pool and an outdoor fountain). Should it be grounded at the street? Are there some code restrictions on that?
Thanks in advance for your responses.
bflowers

Showing 1 response by bob_bundus

Same conduit is alright.
It would be ideal if the circuits pairs were each twisted (spiraled hot + neutral) for mimimized noise induction between them. However it's done, so don't worry about that. If ground conductors are separate, then they should each be spiraled in the opposite direction around the circuit pairs.

Metal conduit is fine; it is good for RFI shielding.

The 'best' conductor is a controversial question: many varying opinions there. #10 Awg. solid THHN is good. A number of upgrade wire types are also available but some are quite expensive; I can't say if that is worthwhile or not.

Your house ground is the same for everything. Multiple grounds locations can cause major problems with loops, and especially regarding lightning issues.

The audio loads are better off on the opposite phase from your motors if possible. But if they're 240V you have no choice.