Dedicated Line Noise Filter?


I don’t know if what I’m seeking exists, so I’m asking the experts.
I have 2 dedicated lines installed; one for analogue, one for digital. They originate at a sub-panel off the main circuit box. The sub-panel is connected by the hot lead and has it’s own ground including a second grounding rod. There is a home surge protector installed at the main circuit box.

I have passive conditioning on both lines for the components, yet I’m still hearing noise thru the speakers (from about two feet away). I live in a city and I suppose it could be dirty power from the grid.
Now to my question; is there a noise filter that can be installed at the site of the circuit panels? My electrician offered a surge protector with noise filtering (plus EMI/RFI), but was very expensive. So, is there a device that can be installed upstream to lower the noise floor?
Many thanks.
128x128lowrider57

Showing 6 responses by jea48

almarg 7,350 posts07-15-2017 1:27pm
The sub-panel is connected by the hot lead and has it’s own ground including a second grounding rod.
Lowrider, my understanding is that a sub-panel should have hot, neutral, and safety ground all wired back to the main service panel, and safety ground (which may or may not be connected from the sub-panel to earth) should only be connected to neutral at the main panel, and NOT at the sub-panel.
Al, you are correct.
The sub panel feeder Hot/s, neutral, and safety equipment ground conductor are all fed from the same main panel.

An Aux earth ground connection, example ground rod, can be installed and connected to the equipment ground bar in the sub panel in addition to the equipment grounding conductor. Again, in addition to the equipment grounding conductor from the main electrical panel, the sub panel is fed from. (I personally do not recommend the addition of an Aux earth ground. Lightning loves them.)

The sub panel feeder neutral conductor/neutral bar can not be bonded, connected to the sub panel metal enclosure or the equipment ground bar. The feeder neutral bar must be left isolated/insulated from the metal sub panel enclosure. (Green bonding screw or neutral bonding strap that came with the panel discarded.)
If the the feeder neutral conductor/neutral bar is bonded to the enclosure/equipment grounding conductor/equipment ground bar then the equipment grounding conductor will be connected in parallel with the feeder neutral conductor. What happens then is the equipment grounding conductor will carry neutral current back to the main electrical panel, or where the service neutral is bonded, connected to the enclose, equipment ground, and earth. Not good for the equipment grounding conductor to carry neutral current.

@lowrider57
IF you feel confident with yourself looking inside the sub panel I can guide you through things to look for. Something that may be wrong with the way the sub panel is wired.

1) Do you have a multi meter?

2) Is the sub panel wired for straight 120V or 120/240V?
What is the approx distance the sub panel is from the main panel, it is fed from?
Any idea what size the feeder wires are?
What size is the breaker, in the main panel, that feeds the sub panel?

3) Turn off the breaker at the main electrical panel that feeds the sub panel.

4) Verify the sub panel is dead. You can check for voltage at the dedicated circuits outlets first. Use the meter, audio equipment, or a table lamp.

5) Remove the panel cover from the sub panel.

6) Verify 100% the sub panel is dead, de-energized. Use your meter set to auto AC volts or an AC voltage scale above the known voltage feeding the panel.
Locate the feeder wires, conductors, and with the meter verify they are dead.

7) What you should see.

Feeder wires that enter the sub panel.
If 120V only,
1 Hot conductor
1 White color neutral conductor
1 equipment grounding conductor

If 120/240V,
2 Hot conductors
1 white neutral conductor
1 equipment grounding conductor.

*One of the two above must exist. If Not post back. Do not go any further.

Hot feeder wire/s, conductor/s connected to the bus/s of the sub panel, or connected to a main breaker installed in the sub panel. Single pole for 120V, 2 pole for 240V.

You will see a neutral bar, with white color insulated wires that connect to it.
You should see the feeder neutral conductor, white in color, connected to the bar. You should also see the dedicated branch circuit white color neutral wires also connected to the bar. The bar should be mounted to a factory installed insulating material. Usually the insulator is black in color.
Look closely at the neutral bar, (or possibly 2 neutral bars that may be mounted on each side of the 2 Hot bus and circuit breakers), for a green colored screw head that is made to bond, connect, the neutral bar to the metal panel enclosure. If you see one IT MUST BE REMOVED. Remove the bonding screw and discard. Next look for any other wire or metal strap that may be bonding the neutral bar to the metal panel enclosure. If you see one REMOVE IT and discard.

No bare wires or green color equipment ground wires should be connected to the neutral bar. Only neutral wires can be connected to the neutral bar of a sub panel.

Next thing to look for is the equipment ground bar. It should be mounted/secured directly to the metal panel enclosure. You should see the feeder equipment grounding conductor connected to the bar. The wire may be bare, green in color, or have green marking tape wrapped around the insulation of the wire. You also should see the bare equipment grounding conductor, wires, of your Romex dedicated branch circuits connected to the ground bar.
If the electrician installed an Aux earth driven ground rod you will see the ground wire, from the ground rod, connected to the equipment ground bar as well. (Again an Aux ground rod serves no real purpose and may do more harm than good. Especially in the event of a lightning storm.)

Any questions?




@lowrider57,

On second thought, if you see the green bonding screw on the neutral bar or a bonding strap connected to the neutral bar that is connected to the metal enclosure, do not remove it.

Post back what you find. Do not change anything in the panel.

Just post back what you see.

cleeds said:
That your contractor didn't know this - and didn't insist on applying for the required electrical construction permit - raises questions about his competency, and whether he's even licensed to perform this work.
I would be willing to bet, in most States electrical permits are not pulled for the limited type of electrical work lowrider57 had done in his home. Just because an electrical permit was not pulled, may not have been pulled, does not mean the electrician did not install his work and use the proper materials to meet NEC, state, county, and or city, electrical codes.