Dedicated Line


I need your advice on a dedicated line installation. I look at my breaker box and see the neutral and ground connected to each other by a cross bar.
1. Should i seperate them?
2. Should i build another ground and connect it to dedicated line only?

Your input is really appreciated.
Thanks
houstonreef

Showing 1 response by gs5556

The bars are connected for a reason. Leave them alone. To answer your questions:

1. If you seperate the bars, then each and every circuit breaker in the panel might not trip properly on fault. Self-explanatory as to the danger.

2. No. Only one ground is permitted for the whole house electrical system by code.

Strongly suggested: talk to an electrician or your local BD inspector before you touch anything, regardless of what you read here.