@immatthewj
Myth is a breaker will trip when the current passing through the breaker reaches its handle rating.
NEMA requirements says a breaker must trip in less that one hour if overloaded 135%. It also says a breaker must trip within 2 minutes if overloaded 200%.
15A breaker X 135% = 20.25A. Can take up to an hour to trip.
15A breaker X 200% = 30A. Can take up to two minutes to trip.
Both calculations above are for constant, continuous, load current.
In most cases the branch circuit wiring is 14 gauge with an ampacity rating of 15 amps for a 15 amp circuit, breaker. (The breaker amperage rating determines the size of the branch circuit. (Not the branch circuit wiring.)
(Old white paper but still holds true for a regular type breaker.)
https://goodsonengineering.com/wp-content/uploads/2017/08/CircuitBreakerMyths_web.pdf
FWIW, in most cases spec grade or better 5-15R (15A receptacles) use the same internal contacts as a 5-20R (20A receptacle). The only difference is the face plate.
For cord and plug connected appliances and equipment NEMA has requirements that manufacturers must follow. To be able to use a 15A plug the FLA of the appliance or equipment can not exceed a continuous load current of 12A. (Continuous is defined as three hours or more.) For most consumer made products manufactures make sure the FLA is 12 amps or less. Why? Because the majority of wall duplex receptacles outlets in residential dwellings are 15 amp... Even though the kitchen, laundry, dinning room, bathroom, and garage, branch circuits are 20 amp, 15 amp receptacle outlets can be used. NEC, two or more on a 20 amp branch circuit. (A duplex receptacle is two.)
If the FLA is greater than 12A continuous the plug must be a 20A. NEMA Says the FLA can not exceed 16A FLA Continuous for a 20A plug .
The face plate on the 15A outlet makes the outlet idiot proof. A 20 amp plug will not plug into it... It prevents a possible 16 amp load from being connected to 14 gauge copper wiring in the wall. A continuous 16 amp load probably would never trip a 15 amp circuit breaker.
FWIW, what you did is electrically safe,... It just doesn’t meet code.